Logic Machine Forum
LM - integration with Mohlenhoff EZR system - Printable Version
+--- Thread: LM - integration with Mohlenhoff EZR system (/showthread.php?tid=320)
LM - integration with Mohlenhoff EZR system - sorin - 13.06.2016
This is an example about how LM can integrate in KNX a Mohlenhoff EZR zone heating/cooling system, via XML (parse/change).
Resident script (to regular read the data from EZR controller via XML):
grp.checkupdate = function(alias, newvalue, dpt, mindelta)
 local curvalue, valdelta
 -- get current object value
 curvalue = grp.getvalue(alias)
 -- value is numeric and delta is specified
 if type(curvalue) == 'number' and type(mindelta) == 'number' then
   newvalue = tonumber(newvalue) or 0
   valdelta = math.abs(curvalue - newvalue)
   -- delta is below minimum, do nothing
   if valdelta < mindelta then
     return
 -- do not send same boolean values
 elseif type(curvalue) == 'boolean' and curvalue == newvalue then
   return
 grp.update(alias, newvalue, dpt)
http = require('socket.http')
url = 'http://192.168.1.111/data/dynamic.xml'
function starttag(p, tag, attr)
 local nr = tonumber(attr.nr)
 table.insert(path, tag)
 if nr then
   nrtag = tag
   table.insert(path, nr)
function endtag(p, tag)
 table.remove(path)
 if tag == nrtag then
   nrtag = nil
   table.remove(path)
function chardata(p, txt)
 local ptr, len
 txt = txt:trim()
 if #txt == 0 then
   return
 ptr = result
 len = #path
 for i, tag in ipairs(path) do
   if i == len then
     ptr[ tag ] = txt
   elseif not ptr[ tag ] then
     ptr[ tag ] = {}
   ptr = ptr[ tag ]
-- current xml tree path
path = {}
-- resulting table
result = {}
-- tag name that contains "nr" attribute
nrtag = nil
lxp = require('lxp')
parser = lxp.new({
 StartElement = starttag,
 EndElement = endtag,
 CharacterData = chardata,
xml = http.request(url)
res = parser:parse(xml or '')
if res then
  log(result.Devices.Device.HEATAREA[ 1 ].HEATAREA_MODE)
  log(result.Devices.Device.HEATAREA[ 1 ].T_ACTUAL)
  log(result.Devices.Device.HEATAREA[ 1 ].T_TARGET)
  log(result.Devices.Device.HEATAREA[ 1 ].PROGRAM_WEEK)
  log(result.Devices.Device.HEATAREA[ 1 ].PROGRAM_WEEKEND)
  log(result.Devices.Device.HEATAREA[ 1 ].PARTY)
  log(result.Devices.Device.HEATAREA[ 1 ].PARTY_REMAININGTIME)
  log(result.Devices.Device.HEATAREA[ 1 ].ISLOCKED)
  log(result.Devices.Device.IODEVICE[ 1 ].SIGNALSTRENGTH)
  log(result.Devices.Device.IODEVICE[ 1 ].BATTERY)
grp.checkupdate('2/1/1', result.Devices.Device.HEATAREA[ 1 ].HEATAREA_MODE, dt.uint8, 1)
grp.checkupdate('2/1/2', result.Devices.Device.HEATAREA[ 1 ].T_ACTUAL, dt.float16, 0.1)
grp.checkupdate('2/1/3', result.Devices.Device.HEATAREA[ 1 ].T_TARGET, dt.float16, 0.1)
grp.checkupdate('2/1/7', result.Devices.Device.HEATAREA[ 1 ].PROGRAM_WEEK, dt.float16, 1)
grp.checkupdate('2/1/8', result.Devices.Device.HEATAREA[ 1 ].PROGRAM_WEEKEND, dt.float16, 1)
grp.checkupdate('2/1/9', result.Devices.Device.HEATAREA[ 1 ].PARTY, dt.float16, 1)
grp.checkupdate('2/1/10', result.Devices.Device.HEATAREA[ 1 ].PARTY_REMAININGTIME, dt.float16, 1)
grp.checkupdate('2/1/12', result.Devices.Device.HEATAREA[ 1 ].ISLOCKED, dt.float16, 1)
grp.checkupdate('2/1/13', result.Devices.Device.IODEVICE[ 1 ].SIGNALSTRENGTH, dt.uint8, 1)
grp.checkupdate('2/1/14', result.Devices.Device.IODEVICE[ 1 ].BATTERY, dt.uint8, 1)
Event script (writing the data to EZR controller when some data are changed in KNX):
setpoint = event.getvalue()
-- format to XY.Z format (1 decimal)
setpoint = string.format('%.1f', setpoint)
url = 'http://192.168.1.111/data/changes.xml'
xml = [[<?xml version="1.0" encoding="UTF-8"?>
<Devices>
 <Device>
   <ID>EZR01233F</ID>
   <HEATAREA nr="1">
     <T_TARGET>]] .. setpoint .. [[</T_TARGET>
   </HEATAREA>
 </Device>
</Devices>]]
socket.http.request(url, xml)