Logic Machine Forum
Multiple PID - Printable Version
+--- Thread: Multiple PID (/showthread.php?tid=558)
Multiple PID - federicocilla71@gmail.com - 16.01.2017
Goodmorning everyone.
I have a problem I can not make more PID function simultaneously.
Can someone help me. Thank you
RE: Multiple PID - admin - 16.01.2017
Like this:
if not p1 then
  p1 = PID:init({
    current = '1/1/1',
    setpoint = '1/1/2',
    output = '1/1/3'
  p2 = PID:init({
    current = '2/1/1',
    setpoint = '2/1/2',
    output = '2/1/3'
p1:run()
p2:run()
RE: Multiple PID - Erwin van der Zwart - 16.01.2017
Try this (see attachments)
RE: Multiple PID - federicocilla71@gmail.com - 17.01.2017
good morning, thanks for the kind risposta.ma I can not upload the files you sent me. Can you help me.
RE: Multiple PID - Erwin van der Zwart - 17.01.2017
The files are not export/import format but manualy created.
Just open them with a text editor (notepad++ or wordpad or something) and create a user lib called 'pid' and a resident script and past the content manualy to them.
thank you so much
still one last question. To slow down a bit the speed of PID how they work the following values? :
     kp = grp.getvalue ('3/3/105'),
     ki = grp.getvalue ('3/3/106'),
     kd = grp.getvalue ('3/3/107'),
Thanks again for your valuable contribution.
This is project / system configuration related, i would start with 0.3 for all and from there fine tune between 0 to 1 if you need to reduce overshoot or need more agresive loops.