Posts: 187
Threads: 43
Joined: Jul 2015
Reputation:
2
05.01.2022, 09:12
(This post was last modified: 05.01.2022, 09:16 by gtsamis.)
Happy new year!
On the trends widget, if i enable the time controls they apear outside of the widget. Is there any fix for it? I would also like to modifty the displayed decimals on value widget.
Posts: 7720
Threads: 42
Joined: Jun 2015
Reputation:
446
We will look into this. For now either disable zooming or set widget width to 3 or 5 units.
Posts: 187
Threads: 43
Joined: Jul 2015
Reputation:
2
I tried only the height... width worked. What about decimal places display?
Posts: 7720
Threads: 42
Joined: Jun 2015
Reputation:
446
New update has been published. See if it fixed the issue for you. Thousands separator (",") has been removed from the trends value display. Decimals cannot be configured at this moment.
Posts: 187
Threads: 43
Joined: Jul 2015
Reputation:
2
(05.01.2022, 09:35)admin Wrote: We will look into this. For now either disable zooming or set widget width to 3 or 5 units.
(06.01.2022, 13:12)admin Wrote: New update has been published. See if it fixed the issue for you. Thousands separator (",") has been removed from the trends value display. Decimals cannot be configured at this moment.
Works fine, thank you.
Posts: 33
Threads: 8
Joined: Feb 2020
Reputation:
0
WOW,
those energy dashbords looks nice!
How do you do this in Wiser?
I have powertags, but not any daily or weekly calculations shown.
To you use the Active Energy resettable kWh an d log this some how?
BR
GIA
Best Regards
NewBee to wiser
Posts: 1759
Threads: 6
Joined: Jul 2015
Reputation:
115
Yes, create trends on the points you want to log and then create a visu in Touch Config, there you can add the live values and trends on a dashboard.
Posts: 33
Threads: 8
Joined: Feb 2020
Reputation:
0
Yeah, I`am using that function,
But how do you get the the daily summations or weekly? Are they custom widgets/tiles, with the summation done in scripting etc?
BR
GIA
Best Regards
NewBee to wiser
Posts: 187
Threads: 43
Joined: Jul 2015
Reputation:
2
06.09.2022, 12:36
(This post was last modified: 06.09.2022, 12:38 by gtsamis.)
(06.09.2022, 11:51)GIA Wrote: Yeah, I`am using that function,
But how do you get the the daily summations or weekly? Are they custom widgets/tiles, with the summation done in scripting etc?
BR
GIA
Intermediate counters are calculated using virtual objects and scripting...
below is a raw event script that runs on the object when it changes at least 1kw... for sure it need tunning but could help as a starting point
Code: myobjects = grp.tag('CalcTotalA')
totalA = 0
for _, object in ipairs(myobjects) do
totalA = totalA + object.value
end
grp.update('Συνολική ένταση (A)',totalA)
-- Get date
now=os.date('*t')
-- system week day starts from sunday, convert it to knx format
now.wday = now.wday == 1 and 7 or now.wday - 1
-- Init counters
initTotalwh = 0
initT1wh = 0
initT2wh = 0
initT3wh = 0
initT4wh = 0
TotalkWh = math.floor(event.getvalue()/1000)
T1kWh = math.floor((grp.getvalue('Ενεργή ενέργεια Τ1 (Wh)') - initT1wh) /1000)
T2kWh = math.floor((grp.getvalue('Ενεργή ενέργεια Τ2 (Wh)') - initT2wh) /1000)
T3kWh = math.floor((grp.getvalue('Ενεργή ενέργεια Τ3 (Wh)') - initT3wh) /1000)
T4kWh = math.floor((grp.getvalue('Ενεργή ενέργεια Τ4 (Wh)') - initT4wh) /1000)
grp.update('Συνολική ενέργεια (kWh)', TotalkWh)
grp.update('Συνολική ενέργεια Τ1 (kWh)', T1kWh)
grp.update('Συνολική ενέργεια Τ2 (kWh)', T2kWh)
grp.update('Συνολική ενέργεια Τ3 (kWh)', T3kWh)
grp.update('Συνολική ενέργεια Τ4 (kWh)', T4kWh)
metinit=storage.get('met:init', 0)
metpt=storage.get('met:pt', 0)
ypt=storage.get('met:year-pt', 0)
ypt1=storage.get('met:year-pt1', 0)
ypt2=storage.get('met:year-pt2', 0)
yct=storage.get('met:year-ct', 0)
yct1=storage.get('met:year-ct1', 0)
yct2=storage.get('met:year-ct2', 0)
mpt=storage.get('met:month-pt', 0)
mpt1=storage.get('met:month-pt1', 0)
mpt2=storage.get('met:month-pt2', 0)
mct=storage.get('met:month-ct', 0)
mct1=storage.get('met:month-ct1', 0)
mct2=storage.get('met:month-ct2', 0)
daypt=storage.get('met:day-pt', 0)
daypt1=storage.get('met:day-pt1', 0)
daypt2=storage.get('met:day-pt2', 0)
dayct=storage.get('met:day-ct', 0)
dayct1=storage.get('met:day-ct1', 0)
dayct2=storage.get('met:day-ct2',0 )
wpt=storage.get('met:week-pt', 0)
wpt1=storage.get('met:week-pt1', 0)
wpt2=storage.get('met:week-pt2', 0)
wct=storage.get('met:week-ct', 0)
wct1=storage.get('met:week-ct1', 0)
wct2=storage.get('met:week-ct2', 0)
ppt=storage.get('met:period-pt', 0)
ppt1=storage.get('met:period-pt1', 0)
ppt2=storage.get('met:period-pt2', 0)
pct=storage.get('met:period-ct', 0)
pct1=storage.get('met:period-ct1', 0)
pct2=storage.get('met:period-ct2', 0)
delta=TotalkWh-metpt
if now.month==1 and now.day==1 and now.hour==0 and now.min<5 then -- Reseting Yearly, Monthly, Daily energy counters
alert('Reseting Yearly, Monthly, Daily energy counters')
grp.write('Επαναφορά μετρητή διακοπών ρεύματος',true)
storage.set('met:year-pt', yct+delta)
grp.write('Ενέργεια προηγούμενου έτους συνολικά (kWh)', yct+delta)
storage.set('met:year-ct', 0)
grp.write('Ενέργεια τρέχοντα έτους συνολικά (kWh)', 0)
storage.set('met:year-pt1', yct1+delta)
grp.write('Ενέργεια προηγούμενου έτους Τ1 (kWh)', yct1+delta)
storage.set('met:year-ct1', 0)
grp.write('Ενέργεια τρέχοντα έτους Τ1 (kWh)', 0)
storage.set('met:year-pt2', yct2+delta)
grp.write('Ενέργεια προηγούμενου έτους Τ2 (kWh)', yct2+delta)
storage.set('met:year-ct2', 0)
grp.write('Ενέργεια τρέχοντα έτους Τ2 (kWh)', 0)
storage.set('met:month-pt', mct+delta)
grp.write('Ενέργεια προηγούμενου μήνα συνολικά (kWh)', mct+delta)
storage.set('met:month-ct', 0)
grp.write('Ενέργεια τρέχοντα μήνα συνολικά (kWh)', 0)
storage.set('met:month-pt1', mct1+delta)
grp.write('Ενέργεια προηγούμενου μήνα Τ1 (kWh)', mct1+delta)
storage.set('met:month-ct1', 0)
grp.write('Ενέργεια τρέχοντα μήνα Τ1 (kWh)', 0)
storage.set('met:month-pt2', mct2+delta)
grp.write('Ενέργεια προηγούμενου μήνα Τ2 (kWh)', mct2+delta)
storage.set('met:month-ct2', 0)
grp.write('Ενέργεια τρέχοντα μήνα Τ2 (kWh)', 0)
storage.set('met:day-pt', dayct+delta)
grp.write('Ενέργεια προηγούμενης ημέρας συνολικά (kWh)', dayct+delta)
storage.set('met:day-ct', 0)
grp.write('Ενέργεια τρέχουσας ημέρας συνολικά (kWh)', 0)
storage.set('met:day-pt1', dayct1+delta)
grp.write('Ενέργεια προηγούμενης ημέρας Τ1 (kWh)', dayct1+delta)
storage.set('met:day-ct1', 0)
grp.write('Ενέργεια τρέχουσας ημέρας Τ1 (kWh)', 0)
storage.set('met:day-pt2', dayct2+delta)
grp.write('Ενέργεια προηγούμενης ημέρας Τ2 (kWh)', dayct2+delta)
storage.set('met:day-ct2', 0)
grp.write('Ενέργεια τρέχουσας ημέρας Τ2 (kWh)', 0)
elseif now.day==1 and now.hour==0 and now.min<5 then -- Reseting Monthly, Daily energy counters
alert('Reseting Monthly, Daily energy counters')
grp.write('Επαναφορά μετρητή διακοπών ρεύματος',true)
storage.set('met:month-pt', mct+delta)
grp.write('Ενέργεια προηγούμενου μήνα συνολικά (kWh)', mct+delta)
storage.set('met:month-ct', 0)
grp.write('Ενέργεια τρέχοντα μήνα συνολικά (kWh)', 0)
storage.set('met:month-pt1', mct1+delta)
grp.write('Ενέργεια προηγούμενου μήνα Τ1 (kWh)', mct1+delta)
storage.set('met:month-ct1', 0)
grp.write('Ενέργεια τρέχοντα μήνα Τ1 (kWh)', 0)
storage.set('met:month-pt2', mct2+delta)
grp.write('Ενέργεια προηγούμενου μήνα Τ2 (kWh)', mct2+delta)
storage.set('met:month-ct2', 0)
grp.write('Ενέργεια τρέχοντα μήνα Τ2 (kWh)', 0)
storage.set('met:day-pt', dayct+delta)
grp.write('Ενέργεια προηγούμενης ημέρας συνολικά (kWh)', dayct+delta)
storage.set('met:day-ct', 0)
grp.write('Ενέργεια τρέχουσας ημέρας συνολικά (kWh)', 0)
storage.set('met:day-pt1', dayct1+delta)
grp.write('Ενέργεια προηγούμενης ημέρας Τ1 (kWh)', dayct1+delta)
storage.set('met:day-ct1', 0)
grp.write('Ενέργεια τρέχουσας ημέρας Τ1 (kWh)', 0)
storage.set('met:day-pt2', dayct2+delta)
grp.write('Ενέργεια προηγούμενης ημέρας Τ2 (kWh)', dayct2+delta)
storage.set('met:day-ct2', 0)
grp.write('Ενέργεια τρέχουσας ημέρας Τ2 (kWh)', 0)
elseif now.hour==0 and now.min<5 then -- Reseting Daily energy counters
alert('Reseting Daily energy counters')
grp.write('Επαναφορά μετρητή διακοπών ρεύματος',true)
storage.set('met:day-pt', dayct+delta)
grp.write('Ενέργεια προηγούμενης ημέρας συνολικά (kWh)', dayct+delta)
storage.set('met:day-ct', 0)
grp.write('Ενέργεια τρέχουσας ημέρας συνολικά (kWh)', 0)
storage.set('met:day-pt1', dayct1+delta)
grp.write('Ενέργεια προηγούμενης ημέρας Τ1 (kWh)', dayct1+delta)
storage.set('met:day-ct1', 0)
grp.write('Ενέργεια τρέχουσας ημέρας Τ1 (kWh)', 0)
storage.set('met:day-pt2', dayct2+delta)
grp.write('Ενέργεια προηγούμενης ημέρας Τ2 (kWh)', dayct2+delta)
storage.set('met:day-ct2', 0)
grp.write('Ενέργεια τρέχουσας ημέρας Τ2 (kWh)', 0)
elseif delta >= 0.2 then -- adding current difference to energy counters
tariff= grp.getvalue('Τρέχον τιμολόγιο')
storage.set('met:pt', metpt+delta)
storage.set('met:year-ct', yct+delta)
grp.write('Ενέργεια τρέχοντα έτους συνολικά (kWh)', yct+delta)
storage.set('met:month-ct', mct+delta)
grp.write('Ενέργεια τρέχοντα μήνα συνολικά (kWh)', mct+delta)
storage.set('met:week-ct', wct+delta)
grp.write('Ενέργεια τρέχουσας εβδομάδας συνολικά (kWh)', wct+delta)
storage.set('met:day-ct', dayct+delta)
grp.write('Ενέργεια τρέχουσας ημέρας συνολικά (kWh)', dayct+delta)
storage.set('met:period-ct', pct+delta)
grp.write('Ενέργεια τρέχουσας περιόδου συνολικά (kWh)', pct+delta)
if tariff==2 then
-- log(string.format('Adding %2.1fkWh to Total and T2 energy counters', delta))
storage.set('met:year-ct2', yct2+delta)
grp.write('Ενέργεια τρέχοντα έτους Τ2 (kWh)', yct2+delta)
storage.set('met:month-ct2', mct2+delta)
grp.write('Ενέργεια τρέχοντα μήνα Τ2 (kWh)', mct2+delta)
storage.set('met:week-ct2', wct2+delta)
grp.write('Ενέργεια τρέχουσας εβδομάδας Τ2 (kWh)', wct2+delta)
storage.set('met:day-ct2', dayct2+delta)
grp.write('Ενέργεια τρέχουσας ημέρας Τ2 (kWh)', dayct2+delta)
storage.set('met:period-ct2', pct2+delta)
grp.write('Ενέργεια τρέχουσας περιόδου Τ2 (kWh)', pct2+delta)
else
-- log(string.format('Adding %2.1fkWh to Total and T1 energy counters', delta))
storage.set('met:year-ct1', yct1+delta)
grp.write('Ενέργεια τρέχοντα έτους Τ1 (kWh)', yct1+delta)
storage.set('met:month-ct1', mct1+delta)
grp.write('Ενέργεια τρέχοντα μήνα Τ1 (kWh)', mct1+delta)
storage.set('met:week-ct1', wct1+delta)
grp.write('Ενέργεια τρέχουσας εβδομάδας Τ1 (kWh)', wct1+delta)
storage.set('met:day-ct1', dayct1+delta)
grp.write('Ενέργεια τρέχουσας ημέρας Τ1 (kWh)', dayct1+delta)
storage.set('met:period-ct1', pct1+delta)
grp.write('Ενέργεια τρέχουσας περιόδου Τ1 (kWh)', pct1+delta)
end
end
if now.wday==1 and now.hour==0 and now.min<5 then -- Reseting Weekly energy counters
alert('Reseting Weekly energy counters')
storage.set('met:week-pt',wct+delta)
grp.write('Ενέργεια προηγούμενης εβδομάδας συνολικά (kWh)', wct+delta)
storage.set('met:week-pt1',wct1+delta)
grp.write('Ενέργεια προηγούμενης εβδομάδας Τ1 (kWh)', wct1+delta)
storage.set('met:week-pt2',wct2+delta)
grp.write('Ενέργεια προηγούμενης εβδομάδας Τ2 (kWh)', wct2+delta)
storage.set('met:week-ct',0)
grp.write('Ενέργεια τρέχουσας εβδομάδας συνολικά (kWh)', 0)
storage.set('met:week-ct1',0)
grp.write('Ενέργεια τρέχουσας εβδομάδας Τ1 (kWh)', 0)
storage.set('met:week-ct2',0)
grp.write('Ενέργεια τρέχουσας εβδομάδας Τ2 (kWh)', 0)
end
Posts: 33
Threads: 8
Joined: Feb 2020
Reputation:
0
NICE, tanx!
As you say, then I have a starting point.
I would never had figured that out my self....
BR
GIA
Best Regards
NewBee to wiser
|