Hi, unfortunately it does not work for me that I assign a date / time object in the visualization a new value.The Date / Time Picker opens but the selected value is not applied. Does anyone have an idea how I can do this (firmware 20221205)
Hello Daniel, attached is the screenrecord,unfortunately no event seems to be triggered either tried with
value = event.getvalue()
log(value)
to display this but nothing happens
11.01.2023, 12:56 (This post was last modified: 11.01.2023, 13:07 by tom77.)
Yes the problem occurs only for date and time
ok I have tested it on another LM there it works ... I reset and see if it works is eh only my test server .... sorry had not thought to test the times where else thanks a lot
Hi all.
I have the same problem. Only the time and date are not written to the bus. The latest firmware. There is a connection to the bus. Other objects are being written.
16.01.2023, 09:19 (This post was last modified: 16.01.2023, 09:24 by spoty2008.)
(16.01.2023, 09:14)Daniel Wrote: Please explain the steps how do you perform the write.
now = os.date('*t')
wday = now.wday == 1 and 7 or now.wday - 1
time = {
day = wday,
hour = now.hour,
minute = now.min,
second = now.sec,
date = {
day = now.day,
month = now.month,
year = now.year,
grp.write('1/0/6', time, dt.time) -- time value
grp.write('1/0/7', date, dt.date) -- date value
log(time)
grp.write('0/4/11', false)
This is a standard script. It works on other logic machines. The problem is only on the current one.
The last line is the address to check that there is a connection and the values are being sent (the values are being sent).
I tried deleting objects in the logic engine and recreating them from ets. Tried to create objects completely manually - nothing helps.
now = os.date('*t')
time = {
day = wday,
hour = now.hour,
minute = now.min,
second = now.sec,
date = {
day = now.day,
month = now.month,
year = now.year,
log(time)
The values of the object in the logic machine change, but nothing is written to the bus. I watch group monitoring from ets.
(16.01.2023, 09:32)admin Wrote: 1/0/7 has incorrect data type, it should be 11. 3 byte date. The date value is written, but it's interpreted as 16:01:23 instead of 16.01.2023.
This I experimented with other objects. Initially, the addresses were with the correct data types. 1/0/2 and 1/0/3
16.01.2023, 10:08 (This post was last modified: 16.01.2023, 10:40 by spoty2008.)
(16.01.2023, 09:57)Daniel Wrote: I tried this and all is working fine for me. What script do you use for this, Any errors?
The whole problem is just that. On others (I tried on 3 different logic machines in different places) with the same firmware and older ones - everything works well.
The script that I use came above the post. In the same script, I turn off the lighting at 0/4/11 and the shutdown works.
(16.01.2023, 12:28)Daniel Wrote: It is all working fine. Maybe it is some ETS issue? Do you have another LM? You could connect it via TP and see if objects are updated.
I have several remote objects. I checked on other logic machines. The same script (usually I use it when there is nowhere to take time, except for the Internet), there is no such problem anywhere. After trying all possible options, I started looking on the forum for a similar problem and was surprised when I found it right away, like tom77.
What else can you recommend? Downgrade is not possible. There is nothing on the LM, except for 1 script.