Posts: 112
Threads: 39
Joined: Jul 2017
Reputation:
1
Hello,
Is there a way to use two power supplies (640mA) in one knx line? Or is there any power supply with higher output than 640mA?
Thank you.
Posts: 4242
Threads: 21
Joined: Aug 2017
Reputation:
183
Hi
I think 640 is max for KNX line. Add repeater and then new PSU.
BR
------------------------------
Ctrl+F5
Posts: 1748
Threads: 6
Joined: Jul 2015
Reputation:
115
09.07.2018, 08:47
(This post was last modified: 09.07.2018, 08:47 by Erwin van der Zwart.)
Hi,
KNX specifies that you can use a power supply on both ends of the line with a minimal distance of 200m between each PSU (to avoid over-current / burned cables on short circuit)
I have seen this in practice and it's very hard to maintain. When you have a power interruption in one of the PSU's the other one will go into overload error and you can only boot it up again by enabling the PSU's at the same time.
My advice is to never do this, and always use a line coupler with new PSU.
BR,
Erwin
Posts: 153
Threads: 12
Joined: Sep 2015
Reputation:
10
you can by PSU 1280 mA (abb has it in their catalog)