This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Turn off light in 4 hours
#7
Another timer example.

Task: If there is 0 sent to grp address AND it stays for 30 min at this value, switch on relay for 3 min. This is used in sauna installation to drain water after sauning is finished.

Event script, input is binary object:

Code:
value = event.getvalue()

-- turn off timer and turn relay off
if value then
 storage.delete('timer')
 grp.write('1/1/1', false)
-- start timer if not already started
else
 timer = storage.get('timer')
 if not timer then
   storage.set('timer', 0)
 end
end

Scheduled script - run every minute:

Code:
-- check if timer is running
timer = storage.get('timer')
if timer then
 timer = timer + 1
 timer.set('timer', timer)

 -- turn relay on after 30 minutes
 if timer == 30 then
   grp.write('1/1/1', true)
 -- turn relay off after 33 minutes  
 elseif timer == 33 then
   grp.write('1/1/1', false)
 end
end
Reply


Messages In This Thread
Turn off light in 4 hours - by RSV4 - 18.07.2015, 10:48
RE: Turn off light in 4 hours - by Pawel - 18.07.2015, 18:51
RE: Turn off light in 4 hours - by admin - 20.07.2015, 06:10
RE: Turn off light in 4 hours - by RSV4 - 20.07.2015, 08:01
RE: Turn off light in 4 hours - by Pawel - 20.07.2015, 09:29
RE: Turn off light in 4 hours - by admin - 21.07.2015, 08:19
RE: Turn off light in 4 hours - by edgars - 22.01.2016, 07:58

Forum Jump: