Modbus TCP HVAC Gateway - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: Modbus TCP HVAC Gateway (/showthread.php?tid=2949) Pages:
1
2
|
RE: Modbus TCP HVAC Gateway - KoBra - 02.12.2020 profile is above. https://forum.logicmachine.net/attachment.php?aid=1912 RE: Modbus TCP HVAC Gateway - Daniel - 02.12.2020 Most likely the "datatype": "float16", is not float only int16 RE: Modbus TCP HVAC Gateway - admin - 02.12.2020 You need to set "datatype": "uint8" where 1-byte for control is needed. Also don't use "datatype": "float16", use "datatype": "int16" with a multiplier set. RE: Modbus TCP HVAC Gateway - KoBra - 02.12.2020 OK Thanks, the temperature values with float are coming in perfectly but i will change them with Int16 and test again. i will do the others with uint8 and test. Thanks RE: Modbus TCP HVAC Gateway - admin - 02.12.2020 From 0 to 20.47 float16 is the same value as int16 / 100. Outside this range you will get invalid values. You can safely use float16 as bus_datatype though. RE: Modbus TCP HVAC Gateway - KoBra - 02.12.2020 Thanks for the support. Solved it. Attached the revised json for the IDU |