Wiser for KNX and modbus problem - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: General (https://forum.logicmachine.net/forumdisplay.php?fid=2) +--- Thread: Wiser for KNX and modbus problem (/showthread.php?tid=3114) Pages:
1
2
|
RE: Wiser for KNX and modbus problem - Kilogica - 24.02.2021 Ideas anyone? It seems almost that the slave 8 (but 9 is the same) respond as slave 130...I see a sort of pattern here since slave 8 and 9 are two PM3250, but I can't find any sense in that behavior... RE: Wiser for KNX and modbus problem - admin - 24.02.2021 The communication errors are caused by cabling, topology and/or noise sources that affect the signal quality. Another possibility is a damaged RS-485 chip on one of the devices. If real-time data acquisition is not needed then some errors during communication are acceptable. RE: Wiser for KNX and modbus problem - Kilogica - 24.02.2021 Topology is correct (we even undo that short branch), cabling I assume it's the same since we use certified cables, could be some noise but with twisted pairs, terminating resistors and signal grounds I don't see how. Thanks for help anyway, I think that it's the best that we can provide in this situation. RE: Wiser for KNX and modbus problem - Daniel - 24.02.2021 Two weeks ago I was helping in one installation. 16 slaves where two were the PM3255 you have. Everything just worked but the cabling was spot on. If you are confident about cables I would disconnect all slaves and try them one by one. |