LogicMachine Forum
SNMP protocol in Logic Machine - Printable Version

+- LogicMachine Forum (https://forum.logicmachine.net)
+-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1)
+--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10)
+--- Thread: SNMP protocol in Logic Machine (/showthread.php?tid=1573)

Pages: 1 2 3 4


RE: SNMP protocol in Logic Machine - Carlos Padilla - 18.07.2019

Attached an example for a data type OCTET STRING. It is important to clarify that if you want to send a value, it must be passed from ascii to hexadecimal and separated by two points (Smile. For example, the asci 30 when passed to hexadecimal is 33:30. On the other hand, when writing the type of data to write, you can use the type of data or the number that represents it, according to the documentation of LUA SNMP (http://luasnmp.luaforge.net/ objects.html), whichever of the two is possible.
Code:
val=event.getvalue() require('snmp') conn, err = snmp.open({   version = snmp.SNMPv1,   community = 'public',   peer = '192.168.0.222', }) assert(conn, err) if val==true then   vbIn = {     {oid = "1.3.6.1.4.1.1248.4.1.1.2.1.0", type=snmp.TYPE_INTEGER, value = "1"},     {oid = "1.3.6.1.4.1.1248.4.1.1.2.2.0", type=2, value = "33:30"}     } vbOut, err, index = conn:set(vbIn)   log(vbOut)   else   vbIn = { {oid = "1.3.6.1.4.1.1248.4.1.1.2.1.0", type=snmp.TYPE_INTEGER, value = "0"}  } vbOut, err, index = conn:set(vbIn)     end conn:close()



RE: SNMP protocol in Logic Machine - DGrandes - 03.11.2019

Hi,

Is there any way to get an entire table by snmp?
I see the table in Mib browser and I can get single value of table but if i try to put table oid value = nil.


RE: SNMP protocol in Logic Machine - DGrandes - 04.11.2019

Hi,

I´ve seen in snmp lua manual that appears different commands but I don´t see getsubtree command.
How can I implement this command to get the table?

Is there any documentation about snmp in logicmachine?


RE: SNMP protocol in Logic Machine - admin - 04.11.2019

Use this code to walk through SNMP:
Code:
function walk(peer, community, version, root)   local snmp = require('snmp')   local session, err = snmp.open({     peer = peer,     community = community or 'public',     version = version or snmp.SNMPv1   })   if not session then     return nil, 'unable to open session: ' .. tostring(err)   end   root = root or '1'   local vb = { oid = root }   local err   local res = {}   while true do     vb, err = session:getnext(vb)     if err then       break     elseif string.find(vb.oid, root) == nil or vb.type == snmp.ENDOFMIBVIEW then       break     else       res[ vb.oid ] = vb.value     end   end   session:close()   if err then     return nil, 'walk failed: ' .. tostring(err)   else     return res   end end res, err = walk('192.168.1.1', 'public', snmp.SNMPv1, '1.0.8802.1.1.2.1.3') log(res, err)

Arguments for walk:
1. remote device IP
2. community, defaults to 'public'
3. version, defaults to v1
4. root SNMP node, defaults to '1'

SNMP library info: http://luasnmp.luaforge.net/


RE: SNMP protocol in Logic Machine - MarcusH - 21.02.2020

Success today! I made a post in this thread https://forum.logicmachine.net/showthread.php?tid=2371

Now i understand the script from this thread. My next question is how to read out the number, i've read out values from tables before, but on this one im a bit stuck.
I get this result and i want to read out the number to a grp address. i see that you use an other way to read it earlier in this thread, but from my knowledge i can do it from this scrip as well.

Code:
res, err = walk('192.168.1.252', 'public', snmp.SNMPv1, '1.3.6.1.4.1.318.1.1.26.6.3.1.6') log(res, err) if type(res) == 'table' then   voltage = res.????? log(voltage)   end


[Image: 4i9Se4X.png]


RE: SNMP protocol in Logic Machine - admin - 21.02.2020

walk is needed when you want to finds all sub-OIDs within a sub-tree.
Have a look at this example:
https://forum.logicmachine.net/showthread.php?tid=1573&pid=9651#pid9651
You just need to provide device IP and OID to group address mapping. Script will then handle reading.


RE: SNMP protocol in Logic Machine - MarcusH - 21.02.2020

Got it Blush Blush
Code:
res, err = walk('192.168.1.252', 'public', snmp.SNMPv1, '1.3.6.1.4.1.318.1.1.26.6.3.1.6') log(res, err) if type(res) == 'table' then   voltage = res["1.3.6.1.4.1.318.1.1.26.6.3.1.6.1"] log(voltage)   end

(21.02.2020, 08:22)admin Wrote: walk is needed when you want to finds all sub-OIDs within a sub-tree.
Have a look at this example:
https://forum.logicmachine.net/showthread.php?tid=1573&pid=9651#pid9651
You just need to provide device IP and OID to group address mapping. Script will then handle reading.
 
Ahh okey, this is an way easier way then. Thanks


RE: SNMP protocol in Logic Machine - DGrandes - 06.03.2020

Hi,

I have a problem with counter64 data type. I can log it but it hasn´t data type and I can´t write in an object.
What can I do??

   


This one works fine:

   

Thanks


RE: SNMP protocol in Logic Machine - admin - 06.03.2020

Use 29. 8 byte signed integer


RE: SNMP protocol in Logic Machine - DGrandes - 06.03.2020

I´ve use it but update a "0" in the object.

   


RE: SNMP protocol in Logic Machine - admin - 06.03.2020

Change object data type to string and check what you get there


RE: SNMP protocol in Logic Machine - DGrandes - 06.03.2020

I´ve tried it too but the same. I haven´t get nothing.


RE: SNMP protocol in Logic Machine - admin - 07.03.2020

Post full script that you are using to read values


RE: SNMP protocol in Logic Machine - DGrandes - 08.03.2020

(07.03.2020, 13:20)admin Wrote: Post full script that you are using to read values
Code:
local IP_Mikrotik = "192.168.2.1" local OID_Mikrotik = {   {'38/5/1',".1.3.6.1.2.1.25.2.3.1.5.65536"}, --Total Memowy   {'38/5/2',".1.3.6.1.2.1.25.2.3.1.6.65536"}, --Used-Memory   {'38/5/3',".1.3.6.1.2.1.25.3.3.1.2.1"}, --CPU Frecuency   {'38/5/5',".1.3.6.1.4.1.14988.1.1.3.14.0"}, --Carga CPU   {'38/5/11',".1.3.6.1.4.1.14988.1.1.14.1.1.2.1"}, --Interface 1 Name   {'38/5/12',".1.3.6.1.4.1.14988.1.1.14.1.1.2.2"}, --Interface 2 Name   {'38/5/13',".1.3.6.1.4.1.14988.1.1.14.1.1.2.3"}, --Interface 3 Name   {'38/5/14',".1.3.6.1.4.1.14988.1.1.14.1.1.2.4"}, --Interface 4 Name   {'38/5/15',".1.3.6.1.4.1.14988.1.1.14.1.1.2.5"}, --Interface 5 Name   {'38/5/16',".1.3.6.1.4.1.14988.1.1.14.1.1.2.6"}, --Interface 6 Name   {'38/5/17',".1.3.6.1.4.1.14988.1.1.14.1.1.2.7"}, --Interface 7 Name   {'38/5/21',".1.3.6.1.4.1.14988.1.1.14.1.1.11.1"}, --Interface 1 TX bytes   {'38/5/22',".1.3.6.1.4.1.14988.1.1.14.1.1.11.2"}, --Interface 2 TX bytes   {'38/5/23',".1.3.6.1.4.1.14988.1.1.14.1.1.11.3"}, --Interface 3 TX bytes   {'38/5/24',".1.3.6.1.4.1.14988.1.1.14.1.1.11.4"}, --Interface 4 TX bytes   {'38/5/25',".1.3.6.1.4.1.14988.1.1.14.1.1.11.5"}, --Interface 5 TX bytes   {'38/5/26',".1.3.6.1.4.1.14988.1.1.14.1.1.11.6"}, --Interface 6 TX bytes   {'38/5/27',".1.3.6.1.4.1.14988.1.1.14.1.1.11.7"}, --Interface 7 TX bytes   {'38/5/31',".1.3.6.1.4.1.14988.1.1.14.1.1.13.1"}, --Interface 1 RX bytes   {'38/5/32',".1.3.6.1.4.1.14988.1.1.14.1.1.13.2"}, --Interface 2 RX bytes   {'38/5/33',".1.3.6.1.4.1.14988.1.1.14.1.1.13.3"}, --Interface 3 RX bytes   {'38/5/34',".1.3.6.1.4.1.14988.1.1.14.1.1.13.4"}, --Interface 4 RX bytes   {'38/5/35',".1.3.6.1.4.1.14988.1.1.14.1.1.13.5"}, --Interface 5 RX bytes   {'38/5/36',".1.3.6.1.4.1.14988.1.1.14.1.1.13.6"}, --Interface 6 RX bytes   {'38/5/37',".1.3.6.1.4.1.14988.1.1.14.1.1.13.7"}, --Interface 7 RX bytes   {'38/5/0',".1.3.6.1.2.1.2.2.1.8.1"}, --Interface 1 Up/Down (Para saber si ISP esta activo } ups1, err = snmp.open{   version = snmp.SNMPv1,   community = "MonitoreoLM",   port = 161,   peer = IP_Mikrotik, } assert(ups1, err) for _, item in ipairs(OID_Mikrotik) do   vbind, err = ups1:get(item[2])   if vbind then     --log(item[1],vbind.value)     grp.checkupdate(item[1], vbind.value)    else     alert('error reading from snmp: ' .. tostring(err))   end end ups1:close()

Solved!. If I convert it to string and again to number it works.

Thanks!


RE: SNMP protocol in Logic Machine - admin - 09.03.2020

Write does not work because SNMP lib uses a special "container" type instead of numbers to store 64-bit values. This will be changed in new versions but for now your approach with tostring/tonumber is correct.


RE: SNMP protocol in Logic Machine - AlexLV - 27.03.2020

Hi,

..admin wrote: ...but for now your approach with tostring/tonumber is correct. How to do it in example above? As I see no all values should be converted tostring/tonumber, just values with digits. Can you explain a little more? I tried to test example above, and I have instead of digital values just zeros...

BR,

Alex

I added conversion for line 45:

grp.checkupdate(item[1], tonumber(tostring(vbind.value)))

but in such case I received all digital values, all strings = nil of course.. How automate this, not to write conversion separately to every line with digit values?

Alex


RE: SNMP protocol in Logic Machine - AlexLV - 28.03.2020

Finally I found how do it working.

Code:
require "snmp" local IP_Mikrotik = "192.168.10.1" local OID_Mikrotik = {   {'38/5/1',".1.3.6.1.2.1.25.2.3.1.5.65536"}, --Total Memowy   {'38/5/2',".1.3.6.1.2.1.25.2.3.1.6.65536"}, --Used-Memory   {'38/5/3',".1.3.6.1.2.1.25.3.3.1.2.1"}, --CPU Frecuency   {'38/5/5',".1.3.6.1.4.1.14988.1.1.3.14.0"}, -- CPU Load   {'38/5/11',".1.3.6.1.4.1.14988.1.1.14.1.1.2.1"}, --Interface 1 Name   {'38/5/12',".1.3.6.1.4.1.14988.1.1.14.1.1.2.2"}, --Interface 2 Name   {'38/5/13',".1.3.6.1.4.1.14988.1.1.14.1.1.2.3"}, --Interface 3 Name   {'38/5/14',".1.3.6.1.4.1.14988.1.1.14.1.1.2.4"}, --Interface 4 Name   {'38/5/15',".1.3.6.1.4.1.14988.1.1.14.1.1.2.5"}, --Interface 5 Name   {'38/5/16',".1.3.6.1.4.1.14988.1.1.14.1.1.2.6"}, --Interface 6 Name   {'38/5/17',".1.3.6.1.4.1.14988.1.1.14.1.1.2.7"}, --Interface 7 Name   {'38/5/21',".1.3.6.1.4.1.14988.1.1.14.1.1.11.1"}, --Interface 1 TX bytes   {'38/5/22',".1.3.6.1.4.1.14988.1.1.14.1.1.11.2"}, --Interface 2 TX bytes   {'38/5/23',".1.3.6.1.4.1.14988.1.1.14.1.1.11.3"}, --Interface 3 TX bytes   {'38/5/24',".1.3.6.1.4.1.14988.1.1.14.1.1.11.4"}, --Interface 4 TX bytes   {'38/5/25',".1.3.6.1.4.1.14988.1.1.14.1.1.11.5"}, --Interface 5 TX bytes   {'38/5/26',".1.3.6.1.4.1.14988.1.1.14.1.1.11.6"}, --Interface 6 TX bytes   {'38/5/27',".1.3.6.1.4.1.14988.1.1.14.1.1.11.7"}, --Interface 7 TX bytes   {'38/5/31',".1.3.6.1.4.1.14988.1.1.14.1.1.13.1"}, --Interface 1 RX bytes   {'38/5/32',".1.3.6.1.4.1.14988.1.1.14.1.1.13.2"}, --Interface 2 RX bytes   {'38/5/33',".1.3.6.1.4.1.14988.1.1.14.1.1.13.3"}, --Interface 3 RX bytes   {'38/5/34',".1.3.6.1.4.1.14988.1.1.14.1.1.13.4"}, --Interface 4 RX bytes   {'38/5/35',".1.3.6.1.4.1.14988.1.1.14.1.1.13.5"}, --Interface 5 RX bytes   {'38/5/36',".1.3.6.1.4.1.14988.1.1.14.1.1.13.6"}, --Interface 6 RX bytes   {'38/5/37',".1.3.6.1.4.1.14988.1.1.14.1.1.13.7"}, --Interface 7 RX bytes   {'38/5/0',".1.3.6.1.2.1.2.2.1.8.1"}, --Interface 1 Up/Down (To find out if ISP is active) } ups1, err = snmp.open{   version = snmp.SNMPv1,   community = "public",   port = 161,   peer = IP_Mikrotik, } assert(ups1, err) for _, item in ipairs(OID_Mikrotik) do   vbind, err = ups1:get(item[2])   if vbind then if tonumber(tostring(vbind.value)) ~=nil then       grp.checkupdate(item[1], tonumber(tostring(vbind.value))) --- Here we receive correct digital values     --log(item[1],vbind.value) else     grp.checkupdate(item[1], vbind.value) --- Here we receive correct string values   end   else     alert('error reading from snmp: ' .. tostring(err))   end end ups1:close()
thanks to admin, he gives us solutions or ways where to possible find answers..


RE: SNMP protocol in Logic Machine - admin - 28.03.2020

A more correct approach of handling counter64 type values:
Code:
if vbind then   value = vbind.value   if type(value) == 'userdata' then     value = tonumber(tostring(value))   end   if value ~= nil then     grp.checkupdate(item[1], value)   end else   alert('error reading from snmp: ' .. tostring(err)) end



RE: SNMP protocol in Logic Machine - AlexLV - 11.04.2020

Hi,
how integrate to last more correct script addon, if data type = "table"
I wanted to add router uptime value, and in log I see it such way:

* arg: 1
* string: 38/5/6
* arg: 2
* table:
["minutes"]
* number: 0
["deciseconds"]
* number: 0
["days"]
* number: 0
["ticks"]
* number: 2165600
["seconds"]
* number: 56
["hours"]
* number: 6

BR,

Alex


RE: SNMP protocol in Logic Machine - admin - 12.04.2020

This will convert table value to a string (for example: 1d 06h 42m).
Code:
if type(value) == 'table' then   value = string.format('%dd %02dh %02dm', value.days or 0, value.hours or 0, value.minutes or 0) end