BACNET IP and IP filters comm - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: BACNET IP and IP filters comm (/showthread.php?tid=6375) |
RE: BACNET IP and IP filters comm - Daniel - 30.04.2026 For Filter to work you must select correct filtering policy, If the selected objects you want to block then select 'drop selected' RE: BACNET IP and IP filters comm - ALEJANDRO - 30.04.2026 So, if, for example, I have 200 group addresses common to LM_1 and LM_4, and I only want communication between 5 of those 200 group addresses, the best thing I can do is: - LM_1 > LM_4 ->> in LM_1 KNX connection >> IP > local > DST group policy >> Drop..... >> Group address list >> enter the 150 group addresses >> OK - LM_4 > LM_1 ->> in LM_4 KNX connection >> IP > local > DST group policy >> Drop..... >> Group address list >> enter the 150 group addresses >> OK Could this be a solution to allow communication only between 5 group addresses stored in LM_1 and LM_4? RE: BACNET IP and IP filters comm - Daniel - 30.04.2026 Other way around, you select accept selected and add this 5 groups. RE: BACNET IP and IP filters comm - ALEJANDRO - 30.04.2026 Could you clarify that last point for me? RE: BACNET IP and IP filters comm - Daniel - 30.04.2026 RE: BACNET IP and IP filters comm - ALEJANDRO - 30.04.2026 Everything's clear now. |