Spacelynk KNX devices load line-wise - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: Spacelynk KNX devices load line-wise (/showthread.php?tid=1065) |
Spacelynk KNX devices load line-wise - pepe - 27.10.2017 Hello everybody
In the appendix, you see a rough principle of Spacelynks and KNX.
I can not load the KNX device 1.1.1 from line 1.2.0, the same problem is when I am with the laptop on IP network and over the multicast address try to load the KNX device 1.1.1 as well as 1.2.1. Both do not work. Clearly there is a solution via ETS IP tunneling to select the respective Spacelynk and load the KNX device on the line, now comes the big but! in a very big project where nearly 150 Spacelynks are used as KNX couplers (and of course Bacnet / Modbus etc.) and I have over 4000 KNX devices is it no longer fun to change the interface every time. Is there a simple solution here? I think hardware should be no problem but most likely the security is to blame? Spacelynk V1.4 / V1.3 Version: 2.1.0 BIG THX RE: Spacelynk KNX devices load line-wise - Jørn - 27.10.2017 At least in ETS5 you can store interface ip for each line. That way, just set it and forget it RE: Spacelynk KNX devices load line-wise - pepe - 28.10.2017 no I am not satisfied with it. so a little detail must be technically feasible RE: Spacelynk KNX devices load line-wise - thientiti01 - 24.11.2017 I think you need active filter function in every KNX coupler |