Modbus multiple registers - Too many data - buuuudzik - 07.03.2018

I've found that there is so limit when I try read the multiple registers. When the number is more than 125 then instead of data there is the info that there is too many data.

Is there a possibility to take more data by one request?

Sometimes useful addresses are very far from them and this is not only about of amount addresses but much more about that I want take all data by one request.


RE: Modbus multiple registers - Too many data - admin - 07.03.2018

It's limited by ModBus standard:
max_read_bits = 2000
max_write_bits = 1968
max_read_registers = 125
max_write_registers = 123


RE: Modbus multiple registers - Too many data - buuuudzik - 07.03.2018

Thanks for answerWink