conection - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Scripting (https://forum.logicmachine.net/forumdisplay.php?fid=8) +--- Thread: conection (/showthread.php?tid=1376) |
conection - balatis - 03.05.2018 hello i have a project with 3 lines, every line have an ip router . wich corect fix is for conect 3 ip routers with a spacelynk and settings? thanks RE: conection - Erwin van der Zwart - 03.05.2018 Hi, 1) Make sure the filter tables are correct in the IP routers and during testing try with all filters open, after that you can add restricted filter settings. 2) Make sure all KNX routers and SL are in the same network scope like 192.168.0.xxx and that all KNX multicast addresses are the same and correct (default = 224.0.23.12). 3) Make sure KNX IP Features is enabled in the SL's KNX settings. 4) Make sure all routers have correct zone / line address like 1.0.0, 1.1.0, 1.2.0, 1.3.0. If you follow steps above it should work.. BR, Erwin RE: conection - balatis - 04.05.2018 hi in the spacelynk , knx connection ,mode wich type i must to put thanks RE: conection - Erwin van der Zwart - 04.05.2018 Hi, Typically when there is a TP connected you set it to TPUART, KNX IP is available as long as KNX IP features is enabled. BR, Erwin RE: conection - balatis - 06.05.2018 (04.05.2018, 12:06)Erwin van der Zwart Wrote: Hi, the conection between ip router and spacelynk will be ethernet .... it is ok TPUART? RE: conection - Erwin van der Zwart - 06.05.2018 Hi, When there are devices connected to the TP connection of the controller you must select TPUART, KNX IP is also working in that setting when the checkbox KNX IP features is enabled. When there are no devices connected (and no KNX power supply) to the TP you should not select TPUART. BR, Erwin RE: conection - balatis - 21.05.2018 hi i try to connect my spacelynk with knx .... i use the ip routing from spacelynk ank knx i have 3 ip routers. i want to have connection with ethernet. when i use the selection ip tunneling it working but i have connection with 1 knx router when i use the selection in the spacelynk ip routing do not work. all the settings is ok. thanks you very mach RE: conection - Daniel - 21.05.2018 Hi Open filter tables on the router and it will work. Your router is blocking telegrams. You can add dummy device to main line and link it with groups you want to see on main line to open selected groups not all. BR RE: conection - balatis - 21.05.2018 i do not central line because every line has 1 ip router every filter is open , work with tunneling..... RE: conection - admin - 21.05.2018 Do you have IP features enabled? Is multicast address the same on all devices? RE: conection - Daniel - 21.05.2018 Even when you use IP routers then you still have main line. KNX always thinks it has it even when it is your IP network. As long multicast is the same on IP router and LM then it must work. I assume you didn't enable some secure communication only or KNX IP secure. RE: conection - balatis - 21.05.2018 here is ok working and second foto do not work RE: conection - Daniel - 21.05.2018 This is not KNX Multicast address, use this 224.0.23.12 RE: conection - balatis - 21.05.2018 it working Daniel thank you very match |