Modbus KNX datatypes doubt - josep - 07.08.2018

Hello, I have a question about data types in Modbus and KNX, many times in Modbus commands appear options to turn on or off something but it make this not using a boolean but an integer, my question is whether it is possible to define the Modbus part as integer but in KNX as a boolean to simplify the config. Thank you very much


RE: Modbus KNX datatypes doubt - admin - 07.08.2018

You can map registers to boolean objects on LM, but only if ON equals 1 and OFF equals 0 in ModBus register.