KNP/TP :Connected ???? - phongvucba - 10.01.2016

On LM3, the "alert" when you press the function.

it appears the words "knp / TP: Connected" very much. interrupting system LM3
At the same time there is also the error log "KNX / TP Transmitter error (send 0 receive 1)"
how to remove "KNX / TP connected" in the alert. ??  interrupting system LM3
thank all!


RE: KNP/TP :Connected ???? - admin - 11.01.2016

KNX/TP might be overloaded, if you have several LMs on a single KNX/TP line they might cause a telegram loop. If this happens then "KNX/IP features" must be disabled in all but one LM.

Otherwise, if KNX/TP is not overloaded, send us your LM for replacement. Please contact us by e-mail for further actions.