Strange behaviour on the knx bus - Tokatubs - 08.03.2019

   

When using the script for time/date i get these telegrams which are sent many times. And i see in the diagnostics that telegrams that are sent on the bus are not longer updated on my logic machine. 

Anybody see this behaviour before. 
Logic machine is placed on the same mainline as the ip router. So i guess all the filtered telegrams reached in my group monitor should reach the LM as well. 
It used to but not anymore. And cant understand why..


RE: Strange behaviour on the knx bus - admin - 08.03.2019

You have a loop there: notice the route cnt field value decreasing. Disable IP features in KNX settings on LM and it should stop.


RE: Strange behaviour on the knx bus - Tokatubs - 08.03.2019

(08.03.2019, 18:47)admin Wrote: You have a loop there: notice the route cnt field value decreasing. Disable IP features in KNX settings on LM and it should stop.

Thanks alot. This is why i love this forum and the product. Have a great weekend.. 