Central statuses - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Scripting (https://forum.logicmachine.net/forumdisplay.php?fid=8) +--- Thread: Central statuses (/showthread.php?tid=220) |
Central statuses - buuuudzik - 16.02.2016 How prepare calculating of central statuses on Logic Machine by event-script and tags? E.g. "1Floor status", "Kitchen status" ... RE: Central statuses - admin - 16.02.2016 Here are 2 functions for getting OR / AND values for binary objects with the same tag. You can then use the result to write out the status. Code: function tag_and(tag)
local objects, result
result = true
objects = grp.tag(tag)
for _, object in ipairs(objects) do
result = result and object.data
return result
function tag_or(tag)
result = false
result = result or object.data
return result
endRE: Central statuses - buuuudzik - 16.02.2016 (16.02.2016, 11:22)admin Wrote: Here are 2 functions for getting OR / AND values for binary objects with the same tag. You can then use the result to write out the status. Thanks
RE: Central statuses - Pawel - 18.02.2016 Is there any solution to prevent executing this function on every tag change? When there is 5 - 10 statuses, there is no problem, but if there is 100 or 200 statuses of whole house, script has to execute 100 time which can slow down LM... RE: Central statuses - buuuudzik - 18.02.2016 (18.02.2016, 08:21)Pawel Wrote: Is there any solution to prevent executing this function on every tag change? Before doing a function you can check if the status of this lamp is the same that the central status. Code: tag="kitchen"
if status1~=central then
tag_or(tag)
end |