PID script - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Scripting (https://forum.logicmachine.net/forumdisplay.php?fid=8) +--- Thread: PID script (/showthread.php?tid=2385) |
PID script - josdegroot - 12.12.2019 Hopefully someone can help me with the following "problem". I would like to use the PID script to control the temperature in one of the bedrooms. The temperature have to be set to 18 degrees... if under setpoint set groupadress ON, if setpoint reached set groupadress OFF. I saw this example script, but the setpoint must not be an groupadress but a fixed value..
This script gives the following error: Resident script:3: attempt to index global 'PID' (a nil value) stack traceback: So I think I made a mistake in the setpoint notation... can somebody help me? Best, Jos RE: PID script - Erwin van der Zwart - 12.12.2019 Hi, You are probably missing the functions that are in the user lib, did you add these to user.pid? To change the setpoint to a static value you probably need to change the function that gets the value from the object in user.pid, but i would advice to create a virtual object and just set the static value there once. Next to that you also need require('user.pid') at the start of your script. There is also a PID block in the FBEditor, maybe this one fits better to your needs. BR, Erwin RE: PID script - josdegroot - 24.12.2019 Thanks Erwin, I'm already a step further and it lookalike the scripts is working. If I run the diagnostics inside ETS I see that the Logic machine sends an ON and OFF message to the group that has to turn the electrical radiator on... but nothing will happen.... The scripts that I'm using? Do you have any idea why the group doesn't respond to the On and Off command? Do I have to set a datatype (switch?) somewhere? Code: -- init pid algorithm
if not p then
p = PID:init({
current = '12/2/1',
setpoint = '32/1/1',
output = '12/0/7'
-- run algorithm
p:run()RE: PID script - Erwin van der Zwart - 25.12.2019 Hi, Does all other bus communication works normal? My first reaction would be that the KNX interface is set to TCP/IP instead of TPUART. BR, Erwin RE: PID script - josdegroot - 25.12.2019 All the scheduled scripts @ the Logic machine work fine. Maybe you can see something @ the screen recording (see attachment) Link to screen recording: https://www.dropbox.com/s/1n1o9me1vb3ku1h/Screen%20Recording%202019-12-25%20at%2010.26.02.mov?dl=0 BTW... on the screen recording the script is off... . That's not the issue .
RE: PID script - Erwin van der Zwart - 25.12.2019 Hi, Can you check the script if it uses grp.update instead of grp.write? grp.update sends to IP but not TP so you can see it on ETS monitor IP side but it’s not send to the TP, i guess that’s the issue you are facing. BR, Erwin RE: PID script - admin - 25.12.2019 From group monitor screenshot it looks like you have KNX TP/IP loop. Do you have any other IP interfaces connected to the same TP line? RE: PID script - josdegroot - 25.12.2019 (25.12.2019, 11:00)Erwin van der Zwart Wrote: Hi, It uses grp.write... to be sure... this is the script Code: PID = {
-- default params
defaults = {
-- invert algorithm, used for cooling
inverted = false,
-- minimum output value
min = 0,
-- maximum output value
max = 100,
-- proportional gain
kp = 1,
-- integral gain
ki = 1,
-- derivative gain
kd = 1,
-- PID init, returns new PID object
function PID:init(params)
local n = setmetatable({}, { __index = PID })
local k, v
-- set user parameters
n.params = params
-- copy parameters that are set by user
for k, v in pairs(PID.defaults) do
if n.params[ k ] == nil then
n.params[ k ] = v
-- reverse gains in inverted mode
if n.params.inverted then
n.params.kp = -n.params.kp
n.params.ki = -n.params.ki
n.params.kd = -n.params.kd
return n
-- resets algorithm on init or a switch back from manual mode
function PID:reset()
-- previous value
self.previous = grp.getvalue(self.params.current)
-- reset iterm
self.iterm = 0
-- last running time
self.lasttime = os.time()
-- clamp iterm
self:clampiterm()
-- clamps iterm value
function PID:clampiterm()
self.iterm = math.max(self.iterm, self.params.min)
self.iterm = math.min(self.iterm, self.params.max)
-- clamp and set new output value
function PID:setoutput()
local t, object, value
self.output = math.max(self.output, self.params.min)
self.output = math.min(self.output, self.params.max)
value = math.floor(self.output)
local t = type(self.params.output)
-- write to output if object is set
if t == 'string' or t == 'table' then
if t == 'string' then
self.params.output = { self.params.output }
for _, output in ipairs(self.params.output) do
grp.write(output, value, dt.scale)
-- algorithm step, returns nil when disabled or no action is required, output value otherwise
function PID:run()
local result
-- get manual mode status
local manual = self.params.manual and grp.getvalue(self.params.manual) or false
-- in manual mode, do nothing
if manual then
self.running = false
-- not in manual, check if reset is required after switching on
elseif not self.running then
self:reset()
self.running = true
-- compute new value if not in manual mode
if self.running then
-- get time between previous and current call
local now = os.time()
self.deltatime = now - self.lasttime
self.lasttime = now
-- run if previous call was at least 1 second ago
if self.deltatime > 0 then
result = self:compute()
return result
-- computes new output value
function PID:compute()
local current, setpoint, deltasc, deltain, output
-- get input values
current = grp.getvalue(self.params.current)
setpoint = grp.getvalue(self.params.setpoint)
-- delta between setpoint and current
deltasc = setpoint - current
-- calculate new iterm
self.iterm = self.iterm + self.params.ki * self.deltatime * deltasc
self:clampiterm()
-- delta between current and previous value
deltain = current - self.previous
-- calculate output value
self.output = self.params.kp * deltasc + self.iterm
self.output = self.output - self.params.kd / self.deltatime * deltain
-- write to output
self:setoutput()
-- save previous value
self.previous = current
return self.output
end(25.12.2019, 11:09)admin Wrote: From group monitor screenshot it looks like you have KNX TP/IP loop. Do you have any other IP interfaces connected to the same TP line? Where can you see this? I'm using a Siemens Ip interface to connect ETS to the TP line. I only would use the logic machine to run scripts.. Can you help me what to change? RE: PID script - Erwin van der Zwart - 25.12.2019 Hi, You don’t need to use the Siemens interface as the controller does the same functions, you can remove it. if you keep using it then disable KNX IP features in the KNX settings. BR, Erwin RE: PID script - josdegroot - 25.12.2019 (25.12.2019, 16:13)Erwin van der Zwart Wrote: Hi, check disabled the checkbox @ the logic machine. Does it make sense that I have the address 1.1.100 for the logic machine? Will check if the script is working fine now. I see that the IP loop is gone . not 4 messages anymore .But the Switch actor doesn't respond to the On or Off messages the logic machine is sending to group 12/0/7. (See attachment) If I put A switch object from a taster in this group everything works fine... RE: PID script - stavros - 10.06.2022 (12.12.2019, 21:22)josdegroot Wrote: Hopefully someone can help me with the following "problem". hello, I have the same problem with you and i don't know what to do to solve it. Do you remember how you solved it? Thank you RE: PID script - admin - 10.06.2022 Add this to Common functions: Code: PID = {
-- default params
defaults = {
inverted = false,
min = 0,
max = 100,
kp = 1,
-- integral gain
ki = 1,
-- derivative gain
kd = 1,
local k, v
n.params = params
n.params[ k ] = v
return n
-- previous value
-- reset iterm
self.iterm = 0
-- clamp iterm
self:clampiterm()
function PID:run()
local result
if manual then
self:reset()
self.running = true
self.lasttime = now
return result
-- get input values
self:clampiterm()
-- write to output
self:setoutput()
return self.output
endRE: PID script - stavros - 10.06.2022 (10.06.2022, 12:54)admin Wrote: Add this to Common functions:thank you for your answer, after this i have the following error "Common functions:331: attempt to perform arithmetic on local 'setpoint' (a nil value) stack traceback: Common functions:331: in function 'compute' Common functions:315: in function 'run' " RE: PID script - admin - 10.06.2022 Check that setpoint object address is valid in the pid script. RE: PID script - stavros - 10.06.2022 (10.06.2022, 13:58)admin Wrote: Check that setpoint object address is valid in the pid script. here is the script -- init pid algorithm if not p then p = PID:init({ current = '32/1/7', setpoint = '32/1/5', manual = '32/1/8', inverted = 0, output = '32/1/6', min=0, max=100, kp=1, ki=1, kd=1 }) end -- run algorithm p:run() and the objects are shown in the attached RE: PID script - admin - 10.06.2022 Restart the script via disable/enable. Also inverted should be false not 0. Because 0 evaluates as "true". RE: PID script - stavros - 10.06.2022 (10.06.2022, 14:12)admin Wrote: Restart the script via disable/enable. Also inverted should be false not 0. Because 0 evaluates as "true". thank you very much, RE: PID script - manos@dynamitec - 12.02.2024 Hello Admin, I am trying to realize a constant light control loop with the PID script you have on the website. I've tried to adjust the kp, ki, kd parameters to make the system stable but there are some issues. Since this not about temperature control and fluctuations to the measured brightness value in the room can be pretty high due to sunny/cloudy day, the system is unstable. I would like to be able to set a min/max step (like +/- 3%) for the value that is written to the bus each control loop even if the PID calculation is resulting to a big difference from the previous value. In this way I would like to avoid positive or negative jumps in the written value. Another thing is to be able to add something like a deadband or hysteresis to the system so if the actual value = setpoint +/- 20 lux for exmple then don't calculate anything. Something similar of what is done now via the manual variable. As my lua scripting skills are basic could you or anyone in this forum please help me figure this out and how the new script will be? Below I am attaching the script I am using now: Code: PID = {
-- default params
defaults = {
inverted = false,
min = 10,
max = 100,
kp = 0.25,
-- integral gain
ki = 0.01,
-- derivative gain
kd = 0.1,
local k, v
n.params = params
n.params[ k ] = v
return n
-- previous value
-- reset iterm
self.iterm = 0
-- clamp iterm
self:clampiterm()
-- output value otherwise
function PID:run()
local result
local manual = false
if self.params.manual then
manual = grp.getvalue(self.params.manual)
if manual then
self:reset()
self.running = true
self.lasttime = now
return result
-- get input values
self:clampiterm()
-- write to output
self:setoutput()
return self.output
endThank you in advance. RE: PID script - Daniel - 13.02.2024 Long time ago I worked on similar solution (not on LM) and to solve this we had to make lux more stable by making an avg form last few values. Try using something like this https://forum.logicmachine.net/showthread.php?tid=4244&pid=27441#pid27441 |