1-bit datapoint decoded value - gtsamis - 28.01.2020

Hi,

I have a paradox alarm gateway that send 1-bit status on the bus, 
When the device sends a telegram with RawDPValue $00 or $01 both LM and ETS decode it the same way as $00=off and $01=on
Sometimes the deivice sends a telegram with RawDPValue $02 or $04 and LM decodes them as on but ETS decodes them as off

The manufacturer manual indicates that the comunication object is 1-bit and the posible values are 0 or 1

My findings are that when the system is disarmed the telegram RawDPValue is $00, regulary armed is $01, stay arm is $02 and force arm is $04

Could this be custom coded 2-bit value or i am missing something?

LM Log
   

ETS monitor
   

Device manual
   


RE: 1-bit datapoint decoded value - Erwin van der Zwart - 28.01.2020

Hi,

They already implemented qubits (:

This must be a 2 bit value, i guess a typo in the manual.

BR,

Erwin


RE: 1-bit datapoint decoded value - gtsamis - 28.01.2020

(28.01.2020, 04:51)Erwin van der Zwart Wrote: Hi,

They already implemented qubits (:

This must be a 2 bit value, i guess a typo in the manual.

BR,

Erwin

Looks like more than a typo  Angel

Thanks