Bacnet tab - OysteinEl - 02.10.2020

Hi 
Im trying to set the LM5 up  as this:
https://openrb.com/logicmachine-as-bacnet-client/

but im not getting the bacnet tab, I have installed the latest firmware, the bacnet package, activated the bacnet in bacnet settings but still the tabline is like this
 
what im trying to achive is to connect the LM5 to a top system. 

Any ideas ?


RE: Bacnet tab - admin - 02.10.2020

Try this package: https://dl.openrb.com/lm-20-imx6/pkg/genohm-scada-bacnet_20190828_imx6.ipk
Do not enable BACnet server. Client and server cannot be used at the same time.