limits when LM as Modbus TCP slave - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: limits when LM as Modbus TCP slave (/showthread.php?tid=3015) |
limits when LM as Modbus TCP slave - ikhy - 25.11.2020 Thanks a lot for the LM resident script like Modbus TCP slave! We can use 125 registers at a time, right? what can i do if i need to read / write more registers? what are the limitations in this? RE: limits when LM as Modbus TCP slave - admin - 25.11.2020 125 registers is ModBus standard limit. But it only applies to a single request. If you want to read/write more then send several requests. RE: limits when LM as Modbus TCP slave - ikhy - 25.11.2020 (25.11.2020, 10:22)admin Wrote: 125 registers is ModBus standard limit. But it only applies to a single request. If you want to read/write more then send several requests.thanks! but what about addressing with multiple requests? will the address of the first register in the second request be 0 again? oh, understand addressing continues RE: limits when LM as Modbus TCP slave - admin - 25.11.2020 Each read request has a starting address and a number of coils/registers to read. The starting address is an absolute value and it does not matter which address was used in previous request. RE: limits when LM as Modbus TCP slave - ikhy - 25.11.2020 so no limits? 65536 registers can be polled? RE: limits when LM as Modbus TCP slave - admin - 25.11.2020 Yes, the whole range can be used. RE: limits when LM as Modbus TCP slave - ikhy - 25.11.2020 thank you! |