Wiser: modbus rtu write to knx tp - PascualNG - 16.09.2021

Hello there,

Is there anyway to send to knx bus tp all the values of modbus rtu? Not only when value changes

Thank you!


RE: Wiser: modbus rtu write to knx tp - Daniel - 16.09.2021

If you don't touch the delta then all will be sent. You can easily flood the bus this way with many registers.


RE: Wiser: modbus rtu write to knx tp - PascualNG - 22.09.2021

(16.09.2021, 09:29)Daniel Wrote: If you don't touch the delta then all will be sent. You can easily flood the bus this way with many registers.

I really need that certain registers always be sent to the bus, regardless of the delta.