KOSTAL Plenticore Modbus Profile - pioneersteffen - 24.09.2021

Hi @all,

I want to integrate my KOSTAL Plenticore inverter via MODBUS to visualize it via TOUCH3.

Does anybody can help me with a tested Modbus configuration?

Many thanks!

Best Regards 
Steffen


RE: KOSTAL Plenticore Modbus Profile - admin - 27.09.2021

You can implement the profile yourself using the generator: https://forum.logicmachine.net/showthread.php?tid=3053
All values are of "register" type and most of them use float32 for "bus_datatype" and "datatype" fields.
Also don't forget to use port 1502 instead of default 502 and set slave ID to 71.


RE: KOSTAL Plenticore Modbus Profile - pioneersteffen - 27.09.2021

Hi Daniel,

many thanks for the hint and providing the tool. I will try my best and post the profile hear after testing it.

Best Regards
Steffen


RE: KOSTAL Plenticore Modbus Profile - pioneersteffen - 03.10.2021

Here is my tested profil just with some important values. But it can be easily adopted.