Logicmachine and Bacnet communication - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Scripting (https://forum.logicmachine.net/forumdisplay.php?fid=8) +--- Thread: Logicmachine and Bacnet communication (/showthread.php?tid=3589) |
Logicmachine and Bacnet communication - stigen - 27.09.2021 Hi! I am using Logicmachine 5 for bacnet communication to a Siemens PXE 50- E.d. There are several values i am reading/writing on bacnet. I tried to have one resident script with all the values for ventilation, and a second resident script for all the values to control the room.(heating, cooling, light++) I also tried to read values from bacnet with a resident script , and then write values to bacnet with event script....(when knx values updates the event script is triggered). This didnt work so fine..... I had the latest backnet package, but removed it and installed and older package that i have on another LM. (that i know works) My question is, do i have to have all in the same resident script? Seems like it collides or something when i have two diffrent script that requires bacnet....or the script runs at the same time.... -S- RE: Logicmachine and Bacnet communication - Daniel - 27.09.2021 Yes everything must be single resident script. RE: Logicmachine and Bacnet communication - stigen - 27.09.2021 Thanks |