Logicmachine and Bacnet communication - stigen - 27.09.2021

Hi!

I am using Logicmachine 5 for bacnet communication to a Siemens PXE 50- E.d.

There are several values i am reading/writing on bacnet.

I tried to have one resident script with all the values for ventilation,  and a second resident script for all the values to control the room.(heating, cooling, light++)



I also tried to read values from bacnet with a resident script , and then write values to bacnet with event script....(when knx values updates the event script is triggered).
This didnt work so fine.....

I had the latest backnet package, but removed it and installed and older package that i have on  another LM. (that i know works)


My question is, do i have to have all in the same resident script?

Seems like it collides or something when i have two diffrent script that requires bacnet....or the script runs at the same time....




-S-


RE: Logicmachine and Bacnet communication - Daniel - 27.09.2021

Yes everything must be single resident script.


RE: Logicmachine and Bacnet communication - stigen - 27.09.2021

Thanks Smile