Logic Machine Forum
LM as main BMS visualization system (Siemens Desigo, Paradox secutiry etc.) - Printable Version

+- Logic Machine Forum (https://forum.logicmachine.net)
+-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1)
+--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10)
+--- Thread: LM as main BMS visualization system (Siemens Desigo, Paradox secutiry etc.) (/showthread.php?tid=3686)



LM as main BMS visualization system (Siemens Desigo, Paradox secutiry etc.) - tpospichal - 16.11.2021

Hello please i need advice.

Client want to integrate KNX, Siemens Desigo (Heating, some lights, ventilation) to the LM visualization. 

Main goals:
  • setup temperatures in rooms, 
  • read temperatures, 
  • control ventilation
  • control lights
  • get system states from heating control room.

It is quite big hotel 30 rooms ant it is mostly controlled by Simens Desigo (Bacnet)

Is LM suitable to do the job like main Visualization?
Can we expect any problems with BACnet, Simens Desigo? We want to import Bacnet Objects directly to he LM or we can use KNX bacnet Gateway.... 


Thank you for some recomandation and advices


RE: LM as main BMS visualization system (Siemens Desigo, Paradox secutiry etc.) - Daniel - 17.11.2021

As I understand in this configuration Siemens Desigo is a Bacnet server. In this case this will not work as LM BACnet Client is only suitable for small integrations. If you can do other way around and make LM Bacnet server and Desigo to be bacnet client then it should will work.


RE: LM as main BMS visualization system (Siemens Desigo, Paradox secutiry etc.) - ivob - 17.11.2021

Siemens Desigo PX, PXC4/5 and Room Automation are all native BACnet controllers out of the box so no extra engineering or gateways are needed.
DXR2 Room controllers with IP connections are recommended.


RE: LM as main BMS visualization system (Siemens Desigo, Paradox secutiry etc.) - tpospichal - 17.11.2021

(17.11.2021, 08:42)ivob Wrote: Siemens Desigo PX, PXC4/5 and Room Automation are all native BACnet controllers out of the box so no extra engineering or gateways are needed.
DXR2 Room controllers with IP connections are recommended.

Thank you for the ansvers. In the building we have PXC controller. Which Is Bacnet server right? 

What about to use Bacnet client do KNX gateway And than make visulalization in LM? Problem Is that owner Will build another rooms which Will be 100% KNX And we need to integrate old part of the building which Is controlled by Desigo. 

Will be this Gateway suitable for this application? 
https://www.intesis.com/products/protocol-translator/bacnet-gateways/bacnet-client-knx-ibox-knx-bac?ordercode=INKNXBAC1000000

Thank you


RE: LM as main BMS visualization system (Siemens Desigo, Paradox secutiry etc.) - Daniel - 17.11.2021

LM will see any KNX telegrams. Yes it should work.