Help me creat feedbacks - Printable Version
+--- Thread: Help me creat feedbacks (/showthread.php?tid=3770)
Help me creat feedbacks - Bitto1998 - 23.12.2021
Hello, I have a problem with Logic Machine 5 Lite. The devices I have in my KNX bus system are very old and do not have group addresses for feedbacks. As a result, the objects I create do not have feedbacks. This means that the status of a luminaire or other switch object is not updated, so I do not have in my management the actual condition of the house. If I am in a remote area I can not know what the real condition of my house is. Is there a way to create virtual feedbacks?
RE: Help me creat feedbacks - Daniel - 23.12.2021
You should do it in ETS and configure your knx devices to send feedback. After that you can import it to LM.
RE: Help me creat feedbacks - admin - 24.12.2021
You can make simple status mapping via a single script. Add feedback tag to all control objects and map an event script to this tag.
Fill mapping table as needed. Table key (1/1/1, 1/1/3 etc) is the control address, key value is either a single status object address or a table containing multiple addresses.
mapping = {   ['1/1/1'] = { '1/1/2', '1/1/9' },     ['1/1/3'] = '1/1/4',   ['1/1/5'] = '1/1/6', } status = mapping[ event.dst ] if type(status) == 'string' then   status = { status } end if type(status) == 'table' then   value = event.getvalue()      for _, addr in ipairs(status) do     grp.checkupdate(addr, value)       end end
You will need additional scripts for more complex situations like setting light value to 0% should set binary status to Off.