problem with 4g modem - Printable Version
+--- Thread: problem with 4g modem (/showthread.php?tid=3839)
Pages: 1 2 3
problem with 4g modem - Frank68 - 31.01.2022
Hello
I asked for the 4g modem to be installed in the reactor, since a customer has only provided me with 4g sim, when the APN returns and the internet connects, I send the emails but I have an error in sending the SMS.
Does the SMS library also have to be modified in order to manage the new modem?
  below the error reported in the offending lines
function sendsms(number, message)   require('socket')   client = socket.udp()   client:sendto(number .. ' ' .. message, '127.0.0.1', 12535) end
RE: problem with 4g modem - admin - 31.01.2022
This script has nothing to do with the SMS sending via modem it simply sends message to the resident script. Post your full resident SMS script and a screenshot from System config > Status > System status > Serial ports.
RE: problem with 4g modem - Frank68 - 31.01.2022
(31.01.2022, 15:30)admin Wrote: This script has nothing to do with the SMS sending via modem it simply sends message to the resident script. Post your full resident SMS script and a screenshot from System config > Status > System status > Serial ports.
resident sms
-- init if not numbers then   require('user.sms')   require('json')   require('socket')   -- allowed numbers, SMS from other numbers will be ignored   numbers = { '3332958126' }   -- port number depends on modem model   comport = 'ttyACM3'   doreset = false -- set to true if USB reset is required before starting any communication   -- if SIM PIN is enabled, uncomment the line below and replace 0000 with SIM PIN   -- pincode = '0000'   -- command parser   parser = function(cmd, sender)     local find, pos, name, mode, offset, value, dvalue, obj, message     cmd = cmd:trim()     mode = cmd:sub(1, 1):upper()     -- invalid request     if mode ~= 'W' and mode ~= 'R' then       return     end     cmd = cmd:sub(3):trim()     -- parse object name/address     find = cmd:sub(1, 1) == '"' and '"' or ' '     offset = find == '"' and 1 or 0     -- pad with space when in read mode     if mode == 'R' and find == ' ' then       cmd = cmd .. ' '     end     -- find object name     pos = cmd:find(find, 1 + offset, true)     -- name end not found, stop     if not pos then       return     end     -- get name part     name = cmd:sub(1 + offset, pos - offset):trim()     if mode == 'W' then       value = cmd:sub(pos + offset):trim()       if #value > 0 then         -- try decoding value         dvalue = json.pdecode(value)         if dvalue ~= nil then           value = dvalue         end         -- send to bus         grp.write(name, value)       end     -- read request     else       obj = grp.find(name)       -- object not known       if not obj then         return       end       -- send read request and wait for an update       obj:read()       os.sleep(1)       -- read new value       value = grp.getvalue(name)       -- got no value       if value == nil then         return       end       -- add object name if specified       if obj.name then         name = string.format('%s (%s)', obj.name, obj.address)       end       message = string.format('Value of %s is %s', name, json.encode(value))       modem:sendsms('+' .. sender, message)     end   end   -- incoming sms handler   handler = function(sms)     --alert('incoming sms: [%s] %s', tostring(sms.sender), tostring(sms.data))     -- sms from known number, call parser     if table.contains(numbers, sms.sender) then       --parser(sms.data, sms.sender)     end   end   -- check local udp server for messages to send   udphandler = function(server)     -- check for local sms to send     local msg = server:receive()     -- got no message     if not msg then       return     end     -- split into number and message     local sep = msg:find(' ')     if not sep then       return     end     --alert('sending sms: ' .. msg)     modem:sendsms(msg:sub(1, sep - 1), msg:sub(sep + 1))   end end -- handle data from modem if modem then   if modem:run() then     udphandler(server)   else     --alert('SMS handler lost connection')     modem:reinit()   end -- modem init else   --alert('SMS handler init')   -- open serial port   modem = AT:init('/dev/' .. comport, doreset)   -- init ok   if modem then     -- set sms handler     modem:setsmshandler(handler)     -- send pin if set     if pincode then       modem:send('AT+CPIN=' .. pincode)       modem:read()     end     -- set to pdu mode     modem:send('AT+CMGF=0')     -- enable sms notifications     modem:send('AT+CNMI=1,1,0,0,0')     -- fixup encoding     modem:send('AT+CSCS="GSM"')     -- delete all saved messages     modem:send('AT+CMGD=1,4')     -- local udp server for sending sms     server = socket.udp()     server:setsockname('127.0.0.1', 12535)     server:settimeout(0.1)     --alert('SMS handler started')   -- init failed   else     --alert('SMS USB init failed')   end end -- init if not numbers then   require('user.sms')   require('json')   require('socket')   -- allowed numbers, SMS from other numbers will be ignored   numbers = { '3332958126' }   -- port number depends on modem model   comport = 'ttyACM3'   doreset = false -- set to true if USB reset is required before starting any communication   -- if SIM PIN is enabled, uncomment the line below and replace 0000 with SIM PIN   -- pincode = '0000'   -- command parser   parser = function(cmd, sender)     local find, pos, name, mode, offset, value, dvalue, obj, message     cmd = cmd:trim()     mode = cmd:sub(1, 1):upper()     -- invalid request     if mode ~= 'W' and mode ~= 'R' then       return     end     cmd = cmd:sub(3):trim()     -- parse object name/address     find = cmd:sub(1, 1) == '"' and '"' or ' '     offset = find == '"' and 1 or 0     -- pad with space when in read mode     if mode == 'R' and find == ' ' then       cmd = cmd .. ' '     end     -- find object name     pos = cmd:find(find, 1 + offset, true)     -- name end not found, stop     if not pos then       return     end     -- get name part     name = cmd:sub(1 + offset, pos - offset):trim()     if mode == 'W' then       value = cmd:sub(pos + offset):trim()       if #value > 0 then         -- try decoding value         dvalue = json.pdecode(value)         if dvalue ~= nil then           value = dvalue         end         -- send to bus         grp.write(name, value)       end     -- read request     else       obj = grp.find(name)       -- object not known       if not obj then         return       end       -- send read request and wait for an update       obj:read()       os.sleep(1)       -- read new value       value = grp.getvalue(name)       -- got no value       if value == nil then         return       end       -- add object name if specified       if obj.name then         name = string.format('%s (%s)', obj.name, obj.address)       end       message = string.format('Value of %s is %s', name, json.encode(value))       modem:sendsms('+' .. sender, message)     end   end   -- incoming sms handler   handler = function(sms)     --alert('incoming sms: [%s] %s', tostring(sms.sender), tostring(sms.data))     -- sms from known number, call parser     if table.contains(numbers, sms.sender) then       --parser(sms.data, sms.sender)     end   end   -- check local udp server for messages to send   udphandler = function(server)     -- check for local sms to send     local msg = server:receive()     -- got no message     if not msg then       return     end     -- split into number and message     local sep = msg:find(' ')     if not sep then       return     end     --alert('sending sms: ' .. msg)     modem:sendsms(msg:sub(1, sep - 1), msg:sub(sep + 1))   end end -- handle data from modem if modem then   if modem:run() then     udphandler(server)   else     --alert('SMS handler lost connection')     modem:reinit()   end -- modem init else   --alert('SMS handler init')   -- open serial port   modem = AT:init('/dev/' .. comport, doreset)   -- init ok   if modem then     -- set sms handler     modem:setsmshandler(handler)     -- send pin if set     if pincode then       modem:send('AT+CPIN=' .. pincode)       modem:read()     end     -- set to pdu mode     modem:send('AT+CMGF=0')     -- enable sms notifications     modem:send('AT+CNMI=1,1,0,0,0')     -- fixup encoding     modem:send('AT+CSCS="GSM"')     -- delete all saved messages     modem:send('AT+CMGD=1,4')     -- local udp server for sending sms     server = socket.udp()     server:setsockname('127.0.0.1', 12535)     server:settimeout(0.1)     --alert('SMS handler started')   -- init failed   else     --alert('SMS USB init failed')   end end
user library
AT = {   -- 7-bit alphabet   alphabet = {     64, 163, 36, 165, 232, 233, 249, 236, 242, 199, 10, 216, 248,     13, 197, 229, 10, 95, 10, 10, 10, 10, 10, 10, 10, 10, 10, 38,     198, 230, 223, 201, 32, 33, 34, 35, 164, 37, 38, 39, 40, 41,     42, 43, 44, 45, 46, 47, 48, 49, 50, 51, 52, 53, 54, 55, 56,     57, 58, 59, 60, 61, 62, 63, 161, 65, 66, 67, 68, 69, 70, 71,     72, 73, 74, 75, 76, 77, 78, 79, 80, 81, 82, 83, 84, 85, 86,     87, 88, 89, 90, 196, 214, 209, 220, 167, 191, 97, 98, 99, 100,     101, 102, 103,  104, 105, 106, 107, 108, 109, 110, 111, 112,     113, 114, 115, 116, 117, 118, 119, 120, 121, 122, 228, 246,     241, 252, 224   },   parsepdu = function(pdu)     local data, len, msg, data, sender, offset, ntype, timestamp     msg = {}     -- offset from service center number     offset = tonumber(pdu:sub(1, 2), 16) * 2     -- sender number length     len = tonumber(pdu:sub(offset + 5, offset + 6), 16)     len = math.ceil(len / 2) * 2     -- sender number type     ntype = tonumber(pdu:sub(offset + 7, offset + 8), 16)     ntype = bit.band(bit.rshift(ntype, 4), 0x07)     -- raw sender number     sender = pdu:sub(offset + 9, offset + len + 8)     -- decode sender number     msg.sender = AT.decodesender(sender, ntype)     -----------------------------------------------     -- timestamp --     offset = offset + len + 13     timestamp = pdu:sub(offset, offset + 13)     timestamp = AT.decodeswapped(timestamp)     msg.timestamp = AT.decodetime(timestamp)     -----------------------------------------------     -- message     len = tonumber(pdu:sub(offset + 14, offset + 15), 16)     data = pdu:sub(offset + 16)     msg.data = AT.decode7bit(data, len)     return msg   end,   -- decode sender address depending on source type   decodesender = function(sender, ntype)     if ntype == 5 then       return AT.decode7bit(sender)     else       return AT.decodeswapped(sender)     end   end,   -- decode time in sms pdu   decodetime = function(timestamp)     local offset, year, time     offset = tonumber(timestamp:sub(13, 14)) or 0     offset = offset * 15 * 60     year = tonumber(timestamp:sub(1, 2))     time = os.time({       year = year < 70 and (2000 + year) or (1900 + year),       month = tonumber(timestamp:sub(3, 4)),       day = tonumber(timestamp:sub(5, 6)),       hour = tonumber(timestamp:sub(7, 8)),       min = tonumber(timestamp:sub(9, 10)),       sec = tonumber(timestamp:sub(11, 12))     }) or os.time()     return time   end,   -- convert swapped number to normal   decodeswapped = function(data)     local i, nr, len, buf     buf = {}     -- real byte length     len = math.floor(data:len() / 2)     -- read 2 bytes at once     for i = 1, len do       -- convert low byte to number       nr = tonumber(data:sub(i * 2, i * 2))       if nr then         table.insert(buf, tostring(nr))       end       -- convert high byte to number       nr = tonumber(data:sub(i * 2 - 1, i * 2 - 1))       if nr then         table.insert(buf, tostring(nr))       end     end     return table.concat(buf)   end,   -- convert from 7 bit char to 8 bit   from7bit = function(c)     if c < 128 then       return string.char(AT.alphabet[ c + 1 ])     else       return ' '     end   end,   -- converts from 7 bit to 8 bit   decode7bit = function(data, len)     local i, o, byte, prev, curr, mask, buf, res     -- convert to binary string     data = lmcore.hextostr(data, true)     -- init vars     o = 0     prev = 0     buf = {}     for i = 1, data:len() do       byte = data:byte(i, i)       -- get 7 bit data       mask = bit.lshift(1, 7 - o) - 1       -- get current chunk       curr = bit.band(byte, mask)       curr = bit.lshift(curr, o)       curr = bit.bor(curr, prev)       -- save bit chunk       prev = bit.rshift(byte, 7 - o)       -- add to buffer       table.insert(buf, AT.from7bit(curr))       -- every 7th step prev will have a full char       if o == 6 then         table.insert(buf, AT.from7bit(prev))         prev = 0       end       o = (o + 1) % 7     end     -- catch last char in buffer     if prev > 0 then       table.insert(buf, AT.from7bit(prev))     end     -- flatten buffer     res = table.concat(buf)     if len then       res = res:sub(1, len)     end     return res   end } function AT:init(dev, reset)   require('serial')   local t = setmetatable({}, { __index = AT })   t.dev = dev   while true do     if t:reinit(30, reset) then       break     else       if reset then         t:reset()       else         return nil       end     end   end   return t end function AT:open(timeout)   local port   while true do     if io.exists(self.dev) then       port = serial.open(self.dev)       if port then         break       end     end     if timeout then       timeout = timeout - 1       if timeout <= 0 then         return false       end     end     os.sleep(1)   end   self.port = port   self.buffer = {}   return true end function AT:reset()   --alert('modem reset')   os.execute('usbreset /dev/bus/usb/001/001') end function AT:reinit(timeout, reset)   local res   if reset then     self:reset()   end   res = self:open(timeout)   self.buffer = {}   return res end function AT:close()   if self.port then     self.port:close()     self.port = nil   end end -- read single line from port function AT:read(timeout)   local char, err, timeout, deftimeout, line   -- default timeout is 1 second, converted to 0.1 sec ticks   timeout = tonumber(timeout) or 1   timeout = timeout * 10   deftimeout = timeout   -- read until got one line or timeout occured   while timeout > 0 do     -- read 1 char     char, err = self.port:read(1, 0.1)     -- got data     if char then       -- got LF, end of line       if char == '\n' then         -- convert to string and empty buffer         line = table.concat(self.buffer)         self.buffer = {}         line = line:trim()         -- return only lines with data         if #line > 0 then           return line         -- reset timeout         else           timeout = deftimeout         end       -- ignore CR       elseif char ~= '\r' then         table.insert(self.buffer, char)       end     -- read timeout     elseif err == 'timeout' then       timeout = timeout - 1     -- other error     else       break     end   end   print('error', err)   return nil, err end -- blocking read until cmd is received function AT:readuntil(cmd, timeout)   local line, err   timeout = timeout or 5   while timeout > 0 do     line, err = self:read()     -- read line ok     if line then       if line == cmd or line == 'COMMAND NOT SUPPORT' or line:match('ERROR') then         return line       else         timeout = timeout - 1         err = 'invalid line'       end     -- timeout     elseif err == 'timeout' then       timeout = timeout - 1     -- other error     else       break     end   end   return nil, err end -- send command to terminal function AT:send(cmd)   local res, err = self.port:write(cmd .. '\r\n')   -- write ok, get local echo   if res then     res, err = self:readuntil(cmd)     self:read()   end   return res, err end -- main handler function AT:run()   local res, err, cmd, pos, sms   res, err = self:read()   if err then     return err == 'timeout'   end   -- check for incoming command   if res:sub(1, 1) ~= '+' then     return true   end   pos = res:find(':', 1, true)   if not pos then     return true   end   -- get command type   cmd = res:sub(2, pos - 1)   -- check only for incoming sms   if cmd ~= 'CMTI' then     return   end   -- read from sim   sms = self:incsms(res)   -- sms seems to be valid, pass to handler if specified   if sms and self.smshandler then     self.smshandler(sms)   end   return true end -- incoming sms handler function AT:incsms(res)   local chunks, index, sms   -- get message index from result   chunks = res:split(',')   if #chunks == 2 then     -- get index and read from it     index = tonumber(chunks[ 2 ])     sms = self:readsms(index)     -- delete sms from store     self:deletesms(index)   end   return sms end -- delete sms at index function AT:deletesms(index)   local cmd, res   -- send delete request   cmd = 'AT+CMGD=' .. index   res = self:send(cmd)   return res end -- read sms at index function AT:readsms(index)   local cmd, res, sms   -- send read request   cmd = 'AT+CMGR=' .. index   res = self:send(cmd)   -- no message at then index   if res == 'OK' then     return nil, 'not found'   end   -- read sms pdu and try decoding   sms = self:read()   res, sms = pcall(AT.parsepdu, sms)   -- decode failed   if not res then     return nil, sms   end   -- wait for ok from modem   self:readuntil('OK')   return sms end function AT:sendsms(number, message)   local cmd, res   -- switch to text mode   self:send('AT+CMGF=1')   -- set number   cmd = string.format('AT+CMGS="%s"', number)   res = self:send(cmd)   -- number seems to be valid   if res ~= 'ERROR' then     -- message and CTRL+Z     self.port:write(message .. string.char(0x1A))     res = self:readuntil('OK')   end   -- switch back to pdu mode   self:send('AT+CMGF=0')   return res end -- set sms handler function AT:setsmshandler(fn)   if type(fn) == 'function' then     self.smshandler = fn   end end table.contains = function(t, v)   for _, i in pairs(t) do     if i == v then       return true     end   end end function sendsms(number, message)   require('socket')   client = socket.udp()   client:sendto(number .. ' ' .. message, '127.0.0.1', 12535) end
RE: problem with 4g modem - admin - 01.02.2022
Replace ttyACM3 with ttyUSB2
RE: problem with 4g modem - Frank68 - 01.02.2022
(01.02.2022, 08:20)admin Wrote: Replace ttyACM3 with ttyUSB2
Nothing
I have this error when i try send sms
User library sms:465: attempt to index global 'client' (a nil value)
stack traceback:
User library sms:465: in function 'sendsms'
but in other reactor works
thanks
Replace the whole sendsms function with this and check if it works. Also check if you have any messages in Logs.
function sendsms(number, message)   local client, err = require('socket').udp()   if client then     client:sendto(number .. ' ' .. message, '127.0.0.1', 12535)     client:close()   else     log('failed to created socket: ' .. tostring(err))   end end
(01.02.2022, 12:18)admin Wrote: Replace the whole sendsms function with this and check if it works. Also check if you have any messages in Logs.
nothinig in log but nothing sms send
You have the same code in the resident script twice, this can lead to errors. You've also commented out all alerts so there's no way of knowing if the script is working or not.
Replace your resident script with this and post what you get in alerts:
-- init if not numbers then   require('user.sms')   require('json')   require('socket')   -- allowed numbers, SMS from other numbers will be ignored   numbers = { '3332958126' }   -- port number depends on modem model   comport = 'ttyACM3'   doreset = false -- set to true if USB reset is required before starting any communication   -- if SIM PIN is enabled, uncomment the line below and replace 0000 with SIM PIN   -- pincode = '0000'   -- command parser   parser = function(cmd, sender)     local find, pos, name, mode, offset, value, dvalue, obj, message     cmd = cmd:trim()     mode = cmd:sub(1, 1):upper()     -- invalid request     if mode ~= 'W' and mode ~= 'R' then       return     end     cmd = cmd:sub(3):trim()     -- parse object name/address     find = cmd:sub(1, 1) == '"' and '"' or ' '     offset = find == '"' and 1 or 0     -- pad with space when in read mode     if mode == 'R' and find == ' ' then       cmd = cmd .. ' '     end     -- find object name     pos = cmd:find(find, 1 + offset, true)     -- name end not found, stop     if not pos then       return     end     -- get name part     name = cmd:sub(1 + offset, pos - offset):trim()     if mode == 'W' then       value = cmd:sub(pos + offset):trim()       if #value > 0 then         -- try decoding value         dvalue = json.pdecode(value)         if dvalue ~= nil then           value = dvalue         end         -- send to bus         grp.write(name, value)       end     -- read request     else       obj = grp.find(name)       -- object not known       if not obj then         return       end       -- send read request and wait for an update       obj:read()       os.sleep(1)       -- read new value       value = grp.getvalue(name)       -- got no value       if value == nil then         return       end       -- add object name if specified       if obj.name then         name = string.format('%s (%s)', obj.name, obj.address)       end       message = string.format('Value of %s is %s', name, json.encode(value))       modem:sendsms('+' .. sender, message)     end   end   -- incoming sms handler   handler = function(sms)     --alert('incoming sms: [%s] %s', tostring(sms.sender), tostring(sms.data))     -- sms from known number, call parser     if table.contains(numbers, sms.sender) then       --parser(sms.data, sms.sender)     end   end   -- check local udp server for messages to send   udphandler = function(server)     -- check for local sms to send     local msg = server:receive()     -- got no message     if not msg then       return     end     -- split into number and message     local sep = msg:find(' ')     if not sep then       return     end     alert('sending sms: ' .. msg)     modem:sendsms(msg:sub(1, sep - 1), msg:sub(sep + 1))   end end -- handle data from modem if modem then   if modem:run() then     udphandler(server)   else     alert('SMS handler lost connection')     modem:reinit()   end -- modem init else   alert('SMS handler init')   -- open serial port   modem = AT:init('/dev/' .. comport, doreset)   -- init ok   if modem then     -- set sms handler     modem:setsmshandler(handler)     -- send pin if set     if pincode then       modem:send('AT+CPIN=' .. pincode)       modem:read()     end     -- set to pdu mode     modem:send('AT+CMGF=0')     -- enable sms notifications     modem:send('AT+CNMI=1,1,0,0,0')     -- fixup encoding     modem:send('AT+CSCS="GSM"')     -- delete all saved messages     modem:send('AT+CMGD=1,4')     -- local udp server for sending sms     server = socket.udp()     server:setsockname('127.0.0.1', 12535)     server:settimeout(0.1)     alert('SMS handler started')   -- init failed   else     alert('SMS USB init failed')   end end
(01.02.2022, 13:35)admin Wrote: You have the same code in the resident script twice, this can lead to errors. You've also commented out all alerts so there's no way of knowing if the script is working or not.
problem to init
Sorry, that was an old script. Replace ttyACM3 with ttyUSB2 and restart the script via disable/enable.
(01.02.2022, 14:56)admin Wrote: Sorry, that was an old script. Replace ttyACM3 with ttyUSB2 and restart the script via disable/enable.
Same error , need som in init script ?
RE: problem with 4g modem - admin - 02.02.2022
Can you provide remote access to your LM?
RE: problem with 4g modem - Frank68 - 02.02.2022
(02.02.2022, 09:13)admin Wrote: Can you provide remote access to your LM?
via zerotier is ok ?
Yes, send your network ID, LM ZeroTier IP and admin password via PM.
Check if it's working now. You had a space after the serial port name so it did not work:
comport = 'ttyUSB2 '
(02.02.2022, 09:53)admin Wrote: Check if it's working now. You had a space after the serial port name so it did not work:
tanks a lot
Hello
For the problem of sending sms I solved with your help in 2 reactor out of 3, in the third with the same scripts, if I text the sms calling send it works, while if it is called from the script the alalrme event does not work, while the mails from the same script do
The alalrme event scripts I checked it are like in the reactor it works in, I'm getting lost and I don't know where.
I accept advice
Thank you
RE: problem with 4g modem - admin - 03.02.2022
Have you replaced the sendsms function as specified? https://forum.logicmachine.net/showthread.php?tid=3839&pid=24831#pid24831
Do you have anything in alerts and logs?
RE: problem with 4g modem - Frank68 - 03.02.2022
(03.02.2022, 07:27)admin Wrote: Have you replaced the sendsms function as specified? https://forum.logicmachine.net/showthread.php?tid=3839&pid=24831#pid24831
Hello
I found the problem, the phone number had a space at the end for which it was not valid, now I try how to remove the spaces before and after, both for the phone number and if I can also for the email address so as to no longer have the problem.
Thank you
RE: problem with 4g modem - andrepneves@gmail.com - 01.07.2024
We are having the same problem that Frank68 sending SMS.
The LM was working fine but from one day to the other it stop working. We tried changing the comport, factory reset the LM and even tried it on other LM with no result.
On Alert tab we keep getting SMS USB init failed.
Another thing I find strange is that the serial ports don't show on system status (view image).
Our firmware is Version: 20230612.
Thanks for your hel p,
Neves