Problem with function 16 in Spacelynk modbus - Kilogica - 23.03.2022

Hello,

I'm trying to control a Hidew DOS dehumidifier via Modbus, I made this profile:

Code:
{ "product_code": "DOS", "manufacturer": "HIDEW", "description": "Deumidificatore DOS",     "mapping":              [                          {    "name": "Unità On/Off",             "bus_datatype":    "bool",             "address": 0,             "type": "coil",             "write_multiple" : true,             "writable": true             },                      {    "name": "Forzatura Deumidifica",             "bus_datatype":    "bool",             "address": 1,             "type": "coil",             "write_multiple" : true,             "writable": true             },                      {    "name": "Abilititazione Forzatura Deumidifica",             "bus_datatype":    "bool",             "address": 2,             "type": "coil",             "write_multiple" : true,             "writable": true             },                      {    "name": "Forzatura Riscaldamento",             "bus_datatype":    "bool",             "address": 3,             "type": "coil",             "write_multiple" : true,             "writable": true             },                      {    "name": "Abilitazione Forzatura Riscaldamento",             "bus_datatype":    "bool",             "address": 4,             "type": "coil",             "write_multiple" : true,             "writable": true             },                      {    "name": "Reset Allarmi",             "bus_datatype":    "bool",             "address": 5,             "type": "coil",             "write_multiple" : true,             "writable": true             },                      {    "name": "Reset pulizia filtri",             "bus_datatype":    "bool",             "address": 6,             "type": "coil",             "write_multiple" : true,             "writable": true             },                      {    "name": "Forzatura Raffreddamento",             "bus_datatype":    "bool",             "address": 7,             "type": "coil",             "write_multiple" : true,             "writable": true             },                      {    "name": "Abilitazione Forzatura Raffreddamento",             "bus_datatype":    "bool",             "address": 8,             "type": "coil",             "write_multiple" : true,             "writable": true             },                      {    "name": "Stato compressore",             "bus_datatype":    "bool",             "address": 0,             "type": "discreteinput",             "writable": false             },                      {    "name": "Stato valvola acqua",             "bus_datatype":    "bool",             "address": 1,             "type": "discreteinput",             "writable": false             },                      {    "name": "Stato resistenza elettrica",             "bus_datatype":    "bool",             "address": 2,             "type": "discreteinput",             "writable": false             },                      {    "name": "Presenza valvola acqua",             "bus_datatype":    "bool",             "address": 3,             "type": "discreteinput",             "writable": false             },                      {    "name": "Presenza resistenza elettrica",             "bus_datatype":    "bool",             "address": 4,             "type": "discreteinput",             "writable": false             },                      {    "name": "Presenza allarme",             "bus_datatype":    "bool",             "address": 5,             "type": "discreteinput",             "writable": false             },                      {    "name": "Filtri da pulire",             "bus_datatype":    "bool",             "address": 6,             "type": "discreteinput",             "writable": false             },                      {    "name": "Presenza ventilatori elettronici",             "bus_datatype":    "bool",             "address": 7,             "type": "discreteinput",             "writable": false             },                      {    "name": "Presenza opzione sbrinamento gas caldo",             "bus_datatype":    "bool",             "address": 8,             "type": "discreteinput",             "writable": false             },                      {    "name": "Allarme sonda",             "bus_datatype":    "bool",             "address": 9,             "type": "discreteinput",             "writable": false             },                      {    "name": "Allarme alta pressione",             "bus_datatype":    "bool",             "address": 10,             "type": "discreteinput",             "writable": false             },                      {    "name": "Allarme bassa pressione",             "bus_datatype":    "bool",             "address": 11,             "type": "discreteinput",             "writable": false             },                      {    "name": "Allarme macchina scarica",             "bus_datatype":    "bool",             "address": 12,             "type": "discreteinput",             "writable": false             },                      {    "name": "Allarme bassa temperatura per ON compressore",             "bus_datatype":    "bool",             "address": 13,             "type": "discreteinput",             "writable": false             },                      {    "name": "Allarme sovratemperatura resistenza elettrica",             "bus_datatype":    "bool",             "address": 14,             "type": "discreteinput",             "writable": false             },                      {    "name": "Allarme ventilatore",             "bus_datatype":    "bool",             "address": 15,             "type": "discreteinput",             "writable": false             },                      {    "name": "Sbrinamento attivo",             "bus_datatype":    "bool",             "address": 16,             "type": "discreteinput",             "writable": false             },                      {    "name": "Richiesta deumidifica",             "bus_datatype":    "bool",             "address": 17,             "type": "discreteinput",             "writable": false             },                      {    "name": "Richiesta riscaldamento",             "bus_datatype":    "bool",             "address": 18,             "type": "discreteinput",             "writable": false             },                      {    "name": "Richiesta raffreddamento",             "bus_datatype":    "bool",             "address": 19,             "type": "discreteinput",             "writable": false             },                      {    "name": "Presenza controllo riscaldamento",             "bus_datatype":    "bool",             "address": 20,             "type": "discreteinput",             "writable": false             },                      {    "name": "Presenza controllo raffreddamento",             "bus_datatype":    "bool",             "address": 21,             "type": "discreteinput",             "writable": false             },                      {    "name": "Presenza funzione deumidificazione ad aria neutra",             "bus_datatype":    "bool",             "address": 22,             "type": "discreteinput",             "writable": false             },                      {    "name": "Presenza opzione raffreddamento con condensatore remoto",             "bus_datatype":    "bool",             "address": 23,             "type": "discreteinput",             "writable": false             },                      {    "name": "Stato condensatore remoto",             "bus_datatype":    "bool",             "address": 24,             "type": "discreteinput",             "writable": false             },                  {    "name": "Set umidità relativa",             "bus_datatype":    "int16",             "address": 0,             "type": "register",             "write_multiple" : true,             "writable": true,             "units": " %"             },                      {    "name": "Set temperatura",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 1,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                  {    "name": "Ore di attesa promemoria pulizia filtri",             "bus_datatype":    "int16",             "address": 2,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " h"             },                      {    "name": "Velocità ventilatore in ricircolo",             "value_custom":                                     {                                     "1" : "Minima",                                     "2" : "Media",                                     "3" : "Massima"                                 },             "bus_datatype":    "int16",             "address": 3,             "type": "register",             "write_multiple" : true,             "writable": true             },                      {    "name": "Velocità ventilatore in deumidifica",             "value_custom":                                     {                                     "2" : "Media",                                     "3" : "Massima"                                 },             "bus_datatype":    "int16",             "address": 4,             "type": "register",             "write_multiple" : true,             "writable": true             },                      {    "name": "Set sbrinamento statico",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 5,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                      {    "name": "Differenziale sbrinamento statico",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 6,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                      {    "name": "Set sbrinamento gas caldo",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 7,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                      {    "name": "Fine sbrinamento gas caldo",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 8,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                      {    "name": "Offset temperatura ambiente",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 9,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                  {    "name": "Offset umidità ambiente",             "bus_datatype":    "int16",             "address": 10,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " %"             },                      {    "name": "Differenziale on riscaldamento",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 11,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                      {    "name": "Differenziale off riscaldamento",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 12,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                  {    "name": "Differenziale on deumidifica",             "bus_datatype":    "int16",             "address": 13,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " %"             },                  {    "name": "Differenziale off deumidifica",             "bus_datatype":    "int16",             "address": 14,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " %"             },                      {    "name": "Differenziale on raffreddamento",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 15,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                      {    "name": "Differenziale off raffreddamento",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 16,             "type": "register",             "write_multiple": true,             "writable": true,             "units": " °C"             },                      {    "name": "Stagione",             "value_custom":                                     {                                     "0" : "Inverno",                                     "1" : "Estate",                                     "2" : "Solo Deumidifica"                                 },             "bus_datatype":    "int16",             "address": 17,             "type": "register",             "write_multiple" : true,             "writable": true             },                  {    "name": "Set umidità relativa effettivo",             "bus_datatype":    "int16",             "address": 0,             "type": "inputregister",             "writable": false,             "units": " %"             },                      {    "name": "Set temperatura effettivo",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 1,             "type": "inputregister",             "writable": false,             "units": " °C"             },                      {    "name": "Velocità effettiva ventilatore",             "value_custom":                                     {                                     "0" : "Off",                                     "1" : "Minima",                                     "2" : "Media",                                     "3" : "Massima"                                 },             "bus_datatype":    "int16",             "address": 2,             "type": "inputregister",             "writable": false             },                  {    "name": "Umidità relativa ambiente",             "bus_datatype":    "int16",             "address": 3,             "type": "inputregister",             "writable": false,             "units": " %"             },                      {    "name": "Temperatura ambiente",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 4,             "type": "inputregister",             "writable": false,             "units": " °C"             },                      {    "name": "Temperatura acqua",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 5,             "type": "inputregister",             "writable": false,             "units": " °C"             },                      {    "name": "Temperatura evaporazione",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 6,             "type": "inputregister",             "writable": false,             "units": " °C"             },                      {    "name": "Temperatura sbrinamento",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 7,             "type": "inputregister",             "writable": false,             "units": " °C"             },                      {    "name": "Matricola valore 1",             "bus_datatype":    "int16",             "address": 8,             "type": "inputregister",             "writable": false             },                      {    "name": "Matricola valore 2",             "bus_datatype":    "int16",             "address": 9,             "type": "inputregister",             "writable": false             },                      {    "name": "Matricola valore 3",             "bus_datatype":    "int16",             "address": 10,             "type": "inputregister",             "writable": false             },                      {    "name": "Matricola valore 4",             "bus_datatype":    "int16",             "address": 11,             "type": "inputregister",             "writable": false             },                      {    "name": "Matricola valore 5",             "bus_datatype":    "int16",             "address": 12,             "type": "inputregister",             "writable": false             },                      {    "name": "Matricola valore 6",             "bus_datatype":    "int16",             "address": 13,             "type": "inputregister",             "writable": false             },                      {    "name": "Matricola valore 7",             "bus_datatype":    "int16",             "address": 14,             "type": "inputregister",             "writable": false             },                      {    "name": "Matricola valore 8",             "bus_datatype":    "int16",             "address": 15,             "type": "inputregister",             "writable": false             },                      {    "name": "Matricola valore 9",             "bus_datatype":    "int16",             "address": 16,             "type": "inputregister",             "writable": false             },                      {    "name": "Matricola valore 10",             "bus_datatype":    "int16",             "address": 17,             "type": "inputregister",             "writable": false             },                      {    "name": "Tipo Macchina",             "value_custom":                                     {                                     "0" : "DDS",                                     "1" : "DCS",                                     "2" : "DVS",                                     "3" : "DOS"                                 },             "bus_datatype":    "int16",             "address": 18,             "type": "inputregister",             "writable": false             },                      {    "name": "Taglia Macchina",             "bus_datatype":    "int16",             "address": 19,             "type": "inputregister",             "writable": false             },                      {    "name": "Ore funzionamento macchina",             "bus_datatype":    "int16",             "address": 20,             "type": "inputregister",             "writable": false             },                      {    "name": "Minuti rimanenti per standby",             "bus_datatype":    "int16",             "address": 21,             "type": "inputregister",             "writable": false             },                      {    "name": "Stato accensione macchina",             "value_custom":                                     {                                     "0" : "Off",                                     "1" : "Standby",                                     "2" : "On"                                 },             "bus_datatype":    "int16",             "address": 22,             "type": "inputregister",             "writable": false             },                      {    "name": "Comando Unità",             "value_custom":                                     {                                     "0" : "da display",                                     "1" : "da fasce orarie",                                     "2" : "da remoto",                                     "3" : "da seriale"                                 },             "bus_datatype":    "int16",             "address": 23,             "type": "inputregister",             "writable": false             },                      {    "name": "Taratura ventilatore elettronico",             "bus_datatype":    "int16",             "address": 24,             "type": "inputregister",             "writable": false,             "units": " %"             },                      {    "name": "Stagione effettiva",             "value_custom":                                     {                                     "0" : "Inverno",                                     "1" : "Estate",                                     "2" : "Solo deumidifica"                                 },             "bus_datatype":    "int16",             "address": 25,             "type": "inputregister",             "writable": false             },                  {    "name": "Pressione di evaporazione",             "bus_datatype":    "float16",             "value_multiplier": 0.1,                                     "address": 26,             "type": "inputregister",             "writable": false,             "units": " bar"             }                  ]      }

Something strange is happening:

I have a Modbus TCP bridge (Z-KEY by Seneca) and 3 modbus devices, everything is working fine but when I try to write a holding register (with write_multiple set to true as the manufacturer recommend) it doesn't work. For example, I can read this register, but I can't write it.

Code:
{    "name": "Set umidità relativa",             "bus_datatype":    "int16",             "address": 0,             "type": "register",             "write_multiple" : true,             "writable": true,             "units": " %"             },


I tried with Modscan and everything works fine, also all the coils are managed correctly from Spacelynk...only write holding registers function seems broken.

Any ideas?


RE: Problem with function 16 in Spacelynk modbus - admin - 24.03.2022

Try adding "datatype": "int16" to the mapping entry.


RE: Problem with function 16 in Spacelynk modbus - Kilogica - 29.03.2022

thanks, it works!