Trends of Bacnet objects - olegrz - 08.09.2022

Hi, How I can add Bacnet objects to trend logs ?
I have:

HW: LM5 Lite + Ext (i.MX6)
SW: 20200312


Thank you in advance! KR Oleg


RE: Trends of Bacnet objects - admin - 09.09.2022

What kind of BACnet objects? You can read data from BACnet devices via scripting a map values to group addresses. Then add these addresses to trend logs.
This might be helpful: https://forum.logicmachine.net/showthread.php?tid=3476&pid=22457#pid22457


RE: Trends of Bacnet objects - olegrz - 15.09.2022

Hi, I just upgraded to the latest FW version.
There are 6 bacnet devices  in my project.
From Vitogate I mapped bacnet object to knx group successfully.
By during mapping procedure for AS01 device I faced with error - see attached screen copy.
How I can resolve it?
Thank you in advance! KR Oleg


RE: Trends of Bacnet objects - Daniel - 15.09.2022

BACnet client app can only work with very limited amount of objects. How many objects did you link so far?


RE: Trends of Bacnet objects - olegrz - 15.09.2022

(15.09.2022, 15:26)Daniel Wrote: BACnet client app can only work with very limited amount of objects. How many objects did you link so far?

At this moment I mapped 13 bacnet objects only from Viessmann Vitogate. See attachment.
From Siemens PXC200 & PXC001 controllers I cannot map nothing.
Every time the mentioned above error is generated.
There are more than 300 bacnet objects in In Siemens controllers. In Vitogate their amount less than 100.


RE: Trends of Bacnet objects - Daniel - 16.09.2022

It looks like the app is not going to work here (btw, not done by us) The script option is your way.
https://openrb.com/logicmachine-as-bacnet-client/


RE: Trends of Bacnet objects - olegrz - 17.09.2022

(16.09.2022, 07:37)Daniel Wrote: It looks like the app is not going to work here (btw, not done by us) The script option is your way.
https://openrb.com/logicmachine-as-bacnet-client/

Hi, Daniel
My bacnet configuration is as on b0.png picture.
When I scan network I obtain non-full list of bacnet devices - see b1.png
There is not full list of bacnet objects for AS_01 device (Siemens PXC200 controller) an for Rooftops
Periodically I obtain error message "Cannot run scan while local BACnet server is running on the same portt"- see b2.png
The same message I periodically obtain for Port 47809 also.
Where are my wrong actions?
Thank you
KR Oleg
I


RE: Trends of Bacnet objects - Daniel - 19.09.2022

Do you use BACnet client app and LM bacnet client at the same time?


RE: Trends of Bacnet objects - olegrz - 19.09.2022

(19.09.2022, 07:23)Daniel Wrote: Do you use BACnet client app and LM bacnet client at the same time?

Yes. Today after several attempts I had success in mapping needed bacnet objects to knx groups.
As I understand the main problem is inner delays during reading of bacnet devices. For Vitogate - very quickly but for Siemens PXC200 - very slowly. By the way YABE browser reads the same devices very quickly.