Check script status + modbus link - sx3 - 15.11.2022

Hello,

I have understood how to enable and disable scripts.
But is it possible per read request determine from a 3rd party visualization if a script is enabled or disbled? What would be the best practice to achive this?

As regarding to a earlier post, that I encountered some problem with dropped modbus link - Is it possible to per GA see if modbus link is up or down?
This goes for both TCP and RTU connections.


RE: Check script status + modbus link - Daniel - 15.11.2022

You can use script.status(name) to get script status. Modbus device has a status object.


RE: Check script status + modbus link - sx3 - 15.11.2022

Okey, not able test right now, but...

Code:
res, strScriptStatus = script.status(name)
log(res)

Will return 0 or 1 to the log depending if it's enabled or disabled?

Regarding Modbus, my devices don't have any status object?
Or is it withing the profile in LM? Where I set TCP / RTU and assign a profile?


RE: Check script status + modbus link - admin - 15.11.2022

script.status returns true/false. Status object is in the device settings (connection type, profile, etc), not in the mapping.


RE: Check script status + modbus link - Daniel - 15.11.2022

Here