3 state heating systems - Printable Version
+--- Thread: 3 state heating systems (/showthread.php?tid=4473)
3 state heating systems - electrokinisi - 01.01.2023
Hello guys,
I need some help to prepare the code for the following function.
I have 3 heat pumps and 13 thermostats.
I want the first heat pump to start when 1 to 4 thermostats are requested,
 the second pump to start after 5 to 8 thermostats,
and then the third pump to start when 9 to 13 thermostats are requested.
Thanks in advance .
RE: 3 state heating systems - admin - 02.01.2023
You can use OR gate from this script: https://forum.logicmachine.net/showthread.php?tid=4395&pid=28367#pid28367
RE: 3 state heating systems - electrokinisi - 03.01.2023
Thank you for the answer,
but I didn't explain it exactly.
I want to randomly add the commands of the thermostats and depending on the demand to start the pumps in stages.
RE: 3 state heating systems - admin - 05.01.2023
Attach a common tag to all thermostat on/off objects then attach an event script to this tag. 1/1/1..3 are your heat pump control objects, modify as needed.
objs = grp.tag('thermostat') count = 0 for _, obj in ipairs(objs) do   if obj.value then     count = count + 1   end end grp.write('1/1/1', count >= 1) grp.write('1/1/2', count >= 5) grp.write('1/1/3', count >= 9)
RE: 3 state heating systems - electrokinisi - 21.01.2023
Hi admin thank you very match ...