BACnet scanning - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: BACnet scanning (/showthread.php?tid=448) |
BACnet scanning - Livadi77 - 01.11.2016 Hi, I am trying to scan a BACnet network through LM5Lite (20160927). I have install the respective package (genohm-scada-bacnet 20160628). Scanning does not bring any of the two BACnet /IP devices which are existing to the network. A 3rd party BACnet explorer is working fine with this BACnet network. Do i have to follow a specific workflow in order to scan BACnet networks through LM5Lite? RE: BACnet scanning - admin - 01.11.2016 Are you running BACnet server on the same device? This combination will only work if server is set to run on a non standard port. RE: BACnet scanning - Livadi77 - 03.11.2016 (01.11.2016, 12:42)admin Wrote: Are you running BACnet server on the same device? This combination will only work if server is set to run on a non standard port. So in order for LM to work as a client and also as a Server the BACnet server port must be other than 47808. Is that right? RE: BACnet scanning - admin - 03.11.2016 Correct RE: BACnet scanning - Livadi77 - 04.11.2016 (03.11.2016, 13:08)admin Wrote: CorrectI have changed the port number in BACnet settings tab to 47809. BACnet scanning still does not find any BACnet device. |