Read group address in ETS no value - RSV4 - 04.11.2016

Hi all,

it has been a while since I last fiddled with my KNX installation, so please bear with me if the answer is easy.
I use ayControl as visualisation app, and would like to set the room temperature with a slider. The slider writes the temperature to a group address (Logicmachine only, no connections in ETS), which populates correctly when I check the Logicmachine objects.
However, when I open the ayControl app, the slider stays at its factory default, e.g. it does not read out the group address with the value for the slider. If I change the group address to a "real" ETS group address (meaning an address on a KNX hardware) the slider jumps to that value.
In ETS, when I use the Group Monitor and try to read the group address which is only used in the Logicmachine, I get nothing back.
Any hints?

Many thanks and best regards
Robin


RE: Read group address in ETS no value - Erwin van der Zwart - 05.11.2016

Hi Robin,

Look at this page, i wrote a article how to make a object response on a read request.

http://forum.logicmachine.net/showthread.php?tid=332&pid=1600&highlight=grp.response#pid1600

BR,

Erwin van der Zwart


RE: Read group address in ETS no value - RSV4 - 05.11.2016

Hi Erwin

Works like a charm, many thanks for your quick reply! Great!

Best regards,
Robin