¿IP communication between several controllers with the same ETS database loaded? - edyzee11 - 13.06.2023

Hello, they called me for a guarantee of a project that has 3 LSS100100 connected by IP and the three teams have loaded the same database and only visualize the system in one of them, the client tells me that strange things happen in the operation of the system the orders arrive late and things are turned on without orders etc... What is the best way to communicate the controllers so that the tasks are executed correctly without saturating the CPU's and not generating system failures.


RE: ¿IP communication between several controllers with the same ETS database loaded? - admin - 14.06.2023

Judging from the screenshot your KNX/TP bus is fully loaded. Do you have any other IP routers connected to the same TP line? You either have a loop between KNX/TP and KNX/IP or some incorrect script that's constantly sending telegrams.