N. 4 MODBUS DEVICES ON A RTU - gdimaria - 15.09.2023

Hi, I have 4 modbus devices on RTU 1 (19600 , parity even).

If I add a single device and map it (no matter if the first, second, etc.)  I can read and write on its registers.

if I have more than a single device mapped on the RTU, I can't write anymore...

the cabling should be ok, any idea about the cause?

Thanks

Peppe


RE: N. 4 MODBUS DEVICES ON A RTU - admin - 15.09.2023

Do you have GND connected between all devices? How many registers are mapped? What is the exact error that you are getting when writing?


RE: N. 4 MODBUS DEVICES ON A RTU - gdimaria - 15.09.2023

Each device mapped about fifty registers.

However I solved by lowering the speed to 9600.

Thank you