GCHV Modbus to LM5 - Samer - 24.11.2023

           
Guys, I have problem with GCHV modBus Gateway I have write the script however I can't write
can you please check it . ??

Code:
{
  "manufacturer": "GCHV",
  "description": "test",
  "mapping": [
      {
      "name": "On Off",
      "address": 40003,
      "value_custom": {
        "1": "Off",
        "2": "On"
          },
      "bus_datatype": "float32",
      "datatype": "uint8",
      "type": "register",
  "value_bitmask": "0XC000",
  "writable": true,
      "write_bitmask": true
    },
      {
      "name": "Setting tempreture",
      "address": 40003,
      "bus_datatype": "temperature",
      "datatype": "uint8",
      "type": "register",
  "value_bitmask": "0X001F",
  "writable": true,
      "write_bitmask": true
    },
{
      "name": "Fan speed",
      "address": 40003,
      "value_custom": {
        "1": "low spped",
        "2": "middle spped",
        "4": "high speed",
        "8": "Auto speed(low speed for GEN3+)"
      },
      "bus_datatype": "uint8",
      "datatype": "uint8",
      "type": "register",
  "value_bitmask": "0X01E0",
  "writable": true,
      "write_bitmask": true
    },
{
      "name": "setting mode",
      "address": 40003,
      "value_custom": {
        "1": "cooling mode",
        "2": "dehumidification mode (cooling mode for GEN3+)",
        "4": "Ventilation mode",
        "8": "heating mode",
        "16": "AUTO mode(cooling mode for GEN3+)",
        "9": "floor heating",
        "10": "intelligent floor heating"
      },
      "bus_datatype": "uint8",
      "datatype": "uint16",
      "type": "register",
  "value_bitmask": "0X3E00",
  "writable": true,
      "write_bitmask": true
    }
  ]
}



RE: GCHV Modbus to LM5 - admin - 24.11.2023

To get real holding register address subtract 40001 from the documented address. Set bus_datatype for On/Off to uint8 instead of float32.


RE: GCHV Modbus to LM5 - Samer - 24.11.2023

Sorry, I didn't get it Admin,
what do you meant by "subtract 40001 from the documented address"


RE: GCHV Modbus to LM5 - admin - 24.11.2023

If documented starting address is 40001 then in reality it is 0. All other registers addresses = ADDRESS - 40001.


RE: GCHV Modbus to LM5 - Samer - 24.11.2023

Updated,
you can see the excel attached.
can you show me an example please ??


RE: GCHV Modbus to LM5 - admin - 24.11.2023

First indoor unit holding register addresses are 0 and 1, second - 2 and 3, and so on.


RE: GCHV Modbus to LM5 - Samer - 24.11.2023

Should this works ??

Code:
{
  "manufacturer": "GCHV",
  "description": "test",
  "mapping": [
      {
      "name": "On Off",
      "address": 0,
      "value_custom": {
        "1": "Off",
        "2": "On"
          },
      "bus_datatype": "uint8",
      "datatype": "uint8",
      "type": "register",
  "value_bitmask": "0XC000",
  "writable": true,
      "write_bitmask": true
    },
      {
      "name": "Setting tempreture",
      "address": 0,
      "bus_datatype": "temperature",
      "datatype": "uint8",
      "type": "register",
  "value_bitmask": "0X001F",
  "writable": true,
      "write_bitmask": true
    },
{
      "name": "Fan speed",
      "address": 0,
      "value_custom": {
        "1": "low spped",
        "2": "middle spped",
        "4": "high speed",
        "8": "Auto speed(low speed for GEN3+)"
      },
      "bus_datatype": "uint8",
      "datatype": "uint8",
      "type": "register",
  "value_bitmask": "0X01E0",
  "writable": true,
      "write_bitmask": true
    },
{
      "name": "setting mode",
      "address": 0,
      "value_custom": {
        "1": "cooling mode",
        "2": "dehumidification mode (cooling mode for GEN3+)",
        "4": "Ventilation mode",
        "8": "heating mode",
        "16": "AUTO mode(cooling mode for GEN3+)",
        "9": "floor heating",
        "10": "intelligent floor heating"
      },
      "bus_datatype": "uint8",
      "datatype": "unit8",
      "type": "register",
  "value_bitmask": "0X3E00",
  "writable": true,
      "write_bitmask": true
    }
  ]
}



RE: GCHV Modbus to LM5 - admin - 24.11.2023

Change all datatype entries to uint16, keep bus_datatype unchanged.