Writing problem in MODBUS with profile - Juande - 08.01.2024

I have a problem with modbus function 16, reading works perfectly through the profile, but I can only write through the lua script. With this script I can write: 
Code:
require('luamodbus')
mb = luamodbus.rtu()
mb:open('/dev/RS485-1', 9600, 'N', 8, 1, 'H')
mb:connect()
mb:setslave(20)
mb:writemultipleregisters(20, 1)
mb:close()

and this is the profile I use: 
Code:
{
  "product_code": "eHome",
  "mapping": [
{"address":10,"datatype":"int16","read_swap":"n","bus_datatype":"float16","value_custom":{ },"type":"inputregister","units":"A","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/100","name":"Cargador_1 Intensidad del vehículo por cable -R-"},
{"address":11,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ "1":"A","2":"B","3":"C","4":"D"},"type":"inputregister","units":" ","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/101","name":"Cargador_1 Estado de carga E.V. -R-"},
{"address":12,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ },"type":"inputregister","units":"er","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/102","name":"Cargador_1 Código de error 1 -R-"},
{"address":13,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ },"type":"inputregister","units":"er","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/103","name":"Cargador_1 Código de error 2 -R-"},
{"address":14,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ },"type":"inputregister","units":"er","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/104","name":"Cargador_1 Código de error 3 -R-"},
{"address":15,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ },"type":"inputregister","units":"A","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/105","name":"Cargador_1 Máxima Potencia de alimentación -R-"},
{"address":16,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ },"type":"inputregister","units":"A","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/106","name":"Cargador_1 Establecer máxima potencia de alimentacion -R/W-"},
{"address":17,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ },"type":"inputregister","units":"%","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/107","name":"Cargador_1 Establecer el porcentaje de intensidad de carga -R/W-"},
{"address":18,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ },"type":"inputregister","units":"min","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/108","name":"Cargador_1 Contador de minutos de última carga. -R-"},
{"address":19,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ },"type":"inputregister","units":"min","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/109","name":"Cargador_1 Contador de minutos de carga actual -R-"},
{"address":20,"datatype":"int16","read_swap":"n","bus_datatype":"bool","value_custom":{ },"type":"inputregister","units":" ","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/110","name":"Cargador_1 Inicio de carga del V.E. -R/W-"},
{"address":21,"datatype":"int16","read_swap":"n","bus_datatype":"bool","value_custom":{ },"type":"inputregister","units":" ","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/111","name":"Cargador_1 Parada de carga el V.E.  -R/W-"},
{"address":22,"datatype":"int16","read_swap":"n","bus_datatype":"bool","value_custom":{ },"type":"inputregister","units":" ","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/112","name":"Cargador_1 Parada temporal de la carga. -R/W-"},
{"address":23,"datatype":"int16","read_swap":"n","bus_datatype":"bool","value_custom":{ },"type":"inputregister","units":" ","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/113","name":"Cargador_1 Puerto de carga deshabilitado -R/W-"},
{"address":24,"datatype":"int16","read_swap":"n","bus_datatype":"bool","value_custom":{ },"type":"inputregister","units":" ","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/114","name":"Cargador_1 Control remoto por controlador DLM -R/W-"},
{"address":60,"datatype":"int16","read_swap":"n","bus_datatype":"float16","value_custom":{ },"type":"inputregister","units":"C","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/115","name":"Cargador_1 Valor interno de la temperatura -R-"},
{"address":61,"datatype":"int16","read_swap":"n","bus_datatype":"float16","value_custom":{ },"type":"inputregister","units":"C","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/116","name":"Cargador_1 Calibración de temperatura -R/W-"},
{"address":62,"datatype":"int16","read_swap":"n","bus_datatype":"bool","value_custom":{ },"type":"inputregister","units":" ","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/117","name":"Cargador_1 Activar reducción de corriente por temperatura -R/W-"},
{"address":63,"datatype":"int16","read_swap":"n","bus_datatype":"bool","value_custom":{ },"type":"inputregister","units":" ","value_multiplier":1,"write_multiple":false,"writable":false,"bus_address":"34/0/118","name":"Cargador_1 Activar reducción de corriente -R-"},
{"address":0,"datatype":"int16","read_swap":"n","bus_datatype":"int16","value_custom":{ },"type":"inputregister","units":" ","value_multiplier":1,"write_multiple":true,"writable":true,"bus_address":"34/0/120","name":"Cargador_1 Dirección Periférica -R/W-"}

  ],
  "manufacturer": "CIRCUTOR",
  "name": "eHome",
  "product_range": "Cargador monofasico 7Kw",
  "description": "Cargador monofasico de 7Kw para coche electrico"
}


Please can you tell me where the error is?


RE: Writing problem in MODBUS with profile - admin - 09.01.2024

"inputregister" is read-only. Change type to "register" in mapping entries that should be writable.


RE: Writing problem in MODBUS with profile - Juande - 09.01.2024

ok, thank you very much, it works now!!!