LSS100200 and Bacnet or Modbus TCP - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: General (https://forum.logicmachine.net/forumdisplay.php?fid=2) +--- Thread: LSS100200 and Bacnet or Modbus TCP (/showthread.php?tid=5213) |
LSS100200 and Bacnet or Modbus TCP - djaval - 21.01.2024 Hi, I have 10 LSS100200 on the site, and need to collect data from them to SCADA system. SCADA does support Modbus TCP and BACNET. Initially, project designers choose BACNET to collect data from LSS100200. This was tested by me and fine works, just need to put "Export" checkbox and SCADA reads and writes the data. But now I need two of LSS100200 devices to communicate to Mitsubishi BACNET gateway for freon systems. As far as I learnt from this forum, it is not possible to use at the same time both Bacnet client and server in LSS100200. Which options do I have to communicate at the same time with SCADA and BACNET gateway? Can I implement Modbus TCP Server (for SCADA) and Bacnet client for Mitsubishi at the same time? RE: LSS100200 and Bacnet or Modbus TCP - Daniel - 22.01.2024 On LM you can do both Modbus client https://kb.logicmachine.net/integration/modbus-rtu-tcp-slave/ RE: LSS100200 and Bacnet or Modbus TCP - djaval - 22.01.2024 (22.01.2024, 08:29)Daniel Wrote: On LM you can do both Thanks, Daniel. I tested, it works. Modbus Poll reads and writes ok. By the way, do you know for SE, is there newer version of BACnet client? I have some old one, and cannot download from app store as it is banned for my country. RE: LSS100200 and Bacnet or Modbus TCP - Daniel - 22.01.2024 SE has same version on its server. |