Hi
What is the internal circuit of RS485 in LM4 like? Is the line terminated internally? Or it is in high-impedance state and the termination must be done by external resistor(s)?

In case the line is not internally terminated do you have a recommendation how to correctly terminate the line?

Are RS485 lines electrically isolated between each other and to other lines especially to KNX bus?

Thank you


RE: RS 485 termination? - admin - 22.12.2016

There's no internal termination. If you need it, then place 120ohm resistors on both line ends. KNX is completely isolated from other system components, RS-485 is not.