Error linking with bacnet objects - batistacaceres - 11.03.2024

Hello team:

I am working with Bacnet Client APP in LogicMachine, each time I try to link logicMachine Objects with Bacnet Object this error is showed, as you can see in attachment.
Could you tell me?, What it is wrong?

   

Error: 
Device with ID=1 or its object with ID = 1_0 doesn´t exist


bestregards

Roger


RE: Error linking with bacnet objects - Daniel - 11.03.2024

How does the object list looks like?


RE: Error linking with bacnet objects - batistacaceres - 11.03.2024

(11.03.2024, 08:50)Daniel Wrote: How does the object list looks like?

I attach it .

   

best regards

Roger


RE: Error linking with bacnet objects - Daniel - 11.03.2024

As this app was created by 3rd party we have very limited options here. I think the app doesn't like the same instance ID being used for different object types.
I would suggest you to use our script solution.
https://kb.logicmachine.net/libraries/bacnet-client/
Use direct connection mode, last example.


RE: Error linking with bacnet objects - batistacaceres - 11.03.2024

(11.03.2024, 09:07)Daniel Wrote: As this app was created by 3rd party we have very limited options here.  I think the app doesn't like the same instance ID being used for different object types.
I would suggest you to use our script solution.
https://kb.logicmachine.net/libraries/bacnet-client/
Use direct connection mode, last example.

Thank you very much...

best regards
Roger


RE: Error linking with bacnet objects - ErkinVural - 23.09.2024

(11.03.2024, 09:07)Daniel Wrote: As this app was created by 3rd party we have very limited options here.  I think the app doesn't like the same instance ID being used for different object types.
I would suggest you to use our script solution.
https://kb.logicmachine.net/libraries/bacnet-client/
Use direct connection mode, last example.

How can I add this code in SE LSS, I don't fully understand, can you help me please? I have the same problem that the friend mentioned.


RE: Error linking with bacnet objects - Daniel - 23.09.2024

You can't, this works only with our bacnet client package and you don't have package installer. Even if everything has to be digitally signed by SE to run on SE HW.


RE: Error linking with bacnet objects - djaval - 23.09.2024

(11.03.2024, 08:55)batistacaceres Wrote:
(11.03.2024, 08:50)Daniel Wrote: How does the object list looks like?

I attach it .



best regards

Roger

Why you use priority 1 for mapping? Don't use it. Better leave 16 as default