Modbus value_delta - alb-smith - 21.06.2024

We believe we have a problem related to the "value_delta" parameter when reading modbus registers.
Is this coefficient evaluated after the multiplication factor?
For example, if I read a power value in W and convert it to kW with a "value_multiplier" of 0.001, is the default/minimum factor 0.2 applied to the kW value? In this case the minimum value of 0.2 may be too large.

Thanks


RE: Modbus value_delta - admin - 21.06.2024

Delta check happens after all calculations are done. The difference between the current object value and the new value is checked.


RE: Modbus value_delta - alb-smith - 21.06.2024

Ok, but if I enter a "value_delta" value less than 0.2 in the modbus profile, which one will be used?

Thaks


RE: Modbus value_delta - admin - 21.06.2024

Right now it cannot be set lower than 0.2. This will be changed in the next version. We'll publish an updated Modbus package once it's ready.


RE: Modbus value_delta - Daniel - 24.06.2024

Install updated Package via System config-System-Package
https://dl.openrb.com/pkg/genohm-scada-modbus_20240621_imx6.ipk
https://dl.openrb.com/pkg/genohm-scada-modbus_20240621_imx6.sig

Clear browser cache after installation.