Modbus value_delta - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: Modbus value_delta (/showthread.php?tid=5480) |
Modbus value_delta - alb-smith - 21.06.2024 We believe we have a problem related to the "value_delta" parameter when reading modbus registers. Is this coefficient evaluated after the multiplication factor? For example, if I read a power value in W and convert it to kW with a "value_multiplier" of 0.001, is the default/minimum factor 0.2 applied to the kW value? In this case the minimum value of 0.2 may be too large. Thanks RE: Modbus value_delta - admin - 21.06.2024 Delta check happens after all calculations are done. The difference between the current object value and the new value is checked. RE: Modbus value_delta - alb-smith - 21.06.2024 Ok, but if I enter a "value_delta" value less than 0.2 in the modbus profile, which one will be used? Thaks RE: Modbus value_delta - admin - 21.06.2024 Right now it cannot be set lower than 0.2. This will be changed in the next version. We'll publish an updated Modbus package once it's ready. RE: Modbus value_delta - Daniel - 24.06.2024 Install updated Package via System config-System-Package https://dl.openrb.com/pkg/genohm-scada-modbus_20240621_imx6.ipk https://dl.openrb.com/pkg/genohm-scada-modbus_20240621_imx6.sig Clear browser cache after installation. |