Modbus - joaodaniel.pereira - 18.07.2024

Hi,
1. I have a suggestion, if we change 1 modbus profile, I need to remote everything related with modbus to update.. is't possible to create a automatic profile refresh or something ?
2. I have one device that send temperature with UINT16 -> 333 ... this it 33.3ºC ... How can I convert the value to have 33.3 ºC in knx?
Example:

the value in the bus is 333 (33.3ºC)

{ "name": "Temperature AQS", "bus_datatype": "int16", "datatype": "int16", "type": "inputregister", "address": 1, "writable": false, "value_multiplier": 0.1, "units": "°C" }

return 33 ºC why ? I convert the value to 33.3 but in the display is an integer value and ignore the decimal part...  I dont have any "float" with 1 byte.. to show the correct value.. 

If I try to multiply with 10, I get 3330 ... but this is not a 2Bytes value to convert to 9.0001..

any solution ?


RE: Modbus - Daniel - 18.07.2024

Change bus_datatype to float16


RE: Modbus - joaodaniel.pereira - 19.07.2024

(18.07.2024, 16:55)Daniel Wrote: Change bus_datatype to float16

And the value for datatype ?


RE: Modbus - admin - 19.07.2024

datatype should stays as is - int16


RE: Modbus - joaodaniel.pereira - 19.07.2024

Thanks, Fixed.
Here:
https://kb.logicmachine.net/misc/modbus-profile/#bus_address

bus_datatype is not clear..
"
bus_datatype
Mapped object data type, key from dt table string/number, required
Example: uint8, scale or float32
"
what datatypes support ?


RE: Modbus - joaodaniel.pereira - 10.02.2025

(19.07.2024, 16:30)joaodaniel.pereira Wrote: Thanks, Fixed.
Here:
https://kb.logicmachine.net/misc/modbus-profile/#bus_address

bus_datatype is not clear..
"
bus_datatype
Mapped object data type, key from dt table string/number, required
Example: uint8, scale or float32
"
what datatypes support ?

Hi,

I have a water meter from BAYLAN  [ NOTE: 4001 = regist 0 ] 

[Image: baylan.png]

[Image: baylan2.png]

And this is my profile: 

moduleID     -> regist 0-1 (uint32) 
consumption -> regist 2-3 (uint32)
Others          -> (uint16)

What is wrong ? 

What is the difference between datatype (what I need as final value ?) and bus_datatype (what is in the bus) ? 

[Image: baylan3.png]

[Image: baylan4.png]


RE: Modbus - Daniel - 10.02.2025

Did you remove the device and add again after modifying the profile?