Modbus Profile incorrect value - AlexLV - 20.01.2025

Hi,

little help is needed. Value I received using my Modbus profile is invalid, please correct me.

Data from manual:

Export power
13010~13011
S32
1W
Power delivered by the inverter to power grid

Part of my profile:

{
      "name": "Export Power",
      "bus_datatype": "float32",
      "datatype": "int32",
      "type": "inputregister",
      "address": 13009,
      "units": "W"
    },

BR, Alex


RE: Modbus Profile incorrect value - admin - 21.01.2025

Use Read test to find correct settings. You might need to use a different swap mode. Why do you map int32 to float32? This is not needed if you are using the value directly without setting value_multiplier.