Zerotier and Local Network - Domoticatorino - 14.05.2025

Good morning,
I am setting a LM in remote by Zerotier. Hence IP address of connection is not the local network.

In the meantime I need to test modbus device on network by TCP/IP communication but devices are in timeout.

Modbus variables are correct and all devices are on line because if I use ping test by LM I can reach them.

Could be the problem related to Zerotier network?

Thanks.

Br


RE: Zerotier and Local Network - Daniel - 14.05.2025

If you use Read test then it is LM sending locally the commands. Zerotier has no influence on this.


RE: Zerotier and Local Network - Domoticatorino - 14.05.2025

(Yesterday, 07:15)Daniel Wrote: If you use Read test then it is LM sending locally the commands. Zerotier has no influence on this.

Hi Daniel,
thank you. I have sort it out. Problem was related to ID modbus device. It was different from 1 and even if on LM communication ID was the same of the device communication was in timeout. 

I changed the ID to 1 and now everything works fine. It is very strange because with modscan I did not find any problem even if ID was different from 1.

Thanks.

Claudio