Acuvim energy meter - FatMax - 16.05.2025

Hi, 

I'm having som issues understadning if my configuration is correct for this meter:

https://www.accuenergy.com/support/modbus-map/#acuvim-ii-modbus-map-3

I'm reading registers 16418-16419 with the use of the profile attached. How can I be sure that both registers are read other than adding datatype float32?


.json   LBC_AcuvimII.json (Size: 1.09 KB / Downloads: 2)



RE: Acuvim energy meter - Daniel - 16.05.2025

This is how you define that LM will read both registers.
Correct this line
"value_multiplier\n\nvalue_multiplier\n\nvalue_multiplier\n\nvalue_multiplier": 0.001,


RE: Acuvim energy meter - FatMax - 16.05.2025

That messes up the kW conversion. The 0,001 should've taken care of that?

   


RE: Acuvim energy meter - admin - 16.05.2025

Most likely you don't need multiplier at all. What value is returned when using Read test?


RE: Acuvim energy meter - FatMax - 16.05.2025

At this very moment reading 16418 as float32 gives me 134130.4375 using read test.

This corresponds great with Value_multiplier in the profile set to 0,001 giving me 133,413 kW. So then I am sure that both registers are read, at least.


RE: Acuvim energy meter - Daniel - 16.05.2025

What is the value on the meter itself?


RE: Acuvim energy meter - FatMax - 16.05.2025

It is at a remote location, so I don't have access to the meter display unfortunately.