False alarm - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Scripting (https://forum.logicmachine.net/forumdisplay.php?fid=8) +--- Thread: False alarm (/showthread.php?tid=6060) |
False alarm - CristianAgata - 26.07.2025 Good day, I have a problem with false data, some time the inverter answer 768 in a modbus TCP register (inverter in foult) although it is not in this condiction then in the next reading after about one minute it answer again 20 (system ok). This register generates an event script to test the value and as you can see in the script it generates an alarm. My question: is it possible wait for example wait 2 minutes and check it again before generate the alarm? Code: evento = event.getvalue()
-- scansione se in un inverter c'è l'allarme (check what kind of event value)
data = grp.tag('Allarme')
for i = 1, 18, 1 do
--log(data[i].value)
if data[i].value == 768 then
status = 'error'
log('Inverter in errore : ',data[i]) --who is
break
else
status = 'ok'
end
end
-- invio comando di chiamata (there is an error 768 so make a call with dealers)
if status == 'error' then
grp.checkwrite('Uscite Combinatore - Relay 1',1,1,'Uscite Combinatore - Relay status 1')
log('un inverter è in blocco')
else
grp.checkwrite('Uscite Combinatore - Relay 1',0,1,'Uscite Combinatore - Relay status 1')
--log('tutto ok')
endThanks for any other suggest. BR Cristian RE: False alarm - admin - 28.07.2025 Use a scheduled script instead of event. Set it to run every one or two minutes. Error state will be set only if object has a fault value two times in a row: Code: objs = grp.tag('Allarme')
key = 'errors'
errors = storage.get(key, {})
err = false
for i, obj in ipairs(objs) do
iserr = obj.value == 768
if iserr and errors[i] then
err = true
log('Inverter in errore : ', obj) --who is
end
errors[i] = iserr
end
storage.set(key, errors)
grp.checkwrite('Uscite Combinatore - Relay 1', err, 1, 'Uscite Combinatore - Relay status 1')RE: False alarm - CristianAgata - 28.07.2025 (28.07.2025, 07:40)admin Wrote: Use a scheduled script instead of event. Set it to run every one or two minutes. Error state will be set only if object has a fault value two times in a row:Thanks admin I will load as fast as possible. |