MQTT Status Problem - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: MQTT Status Problem (/showthread.php?tid=6153) |
MQTT Status Problem - savaskorkmaz - 13.10.2025 Hello, We are communicating with a relay module via MQTT. When we connect using MQTT Explorer, we send the value 00 00 00 07 to the topic address inels/set/2C6A6F1070CE/106/02EAD5 to set the relay output to true. When we send 00 00 00 06, the relay becomes false. Meanwhile, we also receive the status information from the topic inels/status/2C6A6F1070CE/106/02EAD5 — if it’s true, the data is 00 00 00 07 00 00, and if it’s false, it’s 00 00 00 06 00 00. Based on this information, I created two points in the Logic Machine MQTT Client — one for the command and one for the status. The issue is that I can send commands from the Logic Machine, but I can’t transfer the status information back to it. I’ve attached screenshots showing my MQTT Client point settings and the MQTT Explorer view. What kind of mistake could I be making in the status configuration? RE: MQTT Status Problem - Daniel - 13.10.2025 Remove the string conversion and in script for in (from MQTT) log(payload) See what you get there RE: MQTT Status Problem - savaskorkmaz - 13.10.2025 Here are the logs as general and as individiual after log(payload) RE: MQTT Status Problem - admin - 13.10.2025 It uses new line instead of space for status value. Use a script for status conversion: Code: if payload:find('07') then RE: MQTT Status Problem - savaskorkmaz - 13.10.2025 It worked. Thx a lot. |