Pid - Printable Version
+--- Thread: Pid (/showthread.php?tid=6245)
Pid - Michael - 12.01.2026
Hello everyone,
I hope you're all well. I'm writing to you because I'm having a problem with a script related to a PI controller for a radiant floor heating system. The system consists of a 0/10 valve and a flow sensor. To prevent the controller from becoming too sensitive to temperature variations, a moving average filter was added. However, despite this precaution, the PID remains very lazy and unstable.
I've attached the script and an image of the configured parameters. The setpoints, proportional, and integral values are adjustable via the supervisory system. I feel like I'm a bit lost in the dark, so I'm counting on your expert help to resolve this situation. I forgot about the Pt1000 sensors read by the KNX module with a 2-minute cyclic variation and a value change of 0.2K, but the valves are 0/10 controlled by the KNX module.
Thank you so much for your support and availability.
Michael
-- ============================================================ -- REGOLATORE PI – MISCELATRICE PAVIMENTO RADIANTE -- SOLO SONDA MANDATA -- ============================================================ --------------------------------------------------------------- -- PARAMETRI BASE (persistenti) --------------------------------------------------------------- local Kp = storage.get('Kp_PINT') or 3.0 local Ki = storage.get('Ki_PINT') or 0.02 local integral = storage.get('integral_PINT') or 0 local last_mode = storage.get('last_mode') --------------------------------------------------------------- -- CONFIGURAZIONE KNX --------------------------------------------------------------- local group_mode        = '5/0/0'    -- 1=inverno / 0=estate local group_in          = '5/2/1'    -- temperatura mandata local group_out         = '5/0/1'    -- 0–10 V miscelatrice local group_set_winter  = '5/2/4' local group_set_summer  = '5/2/5' local group_kp          = '5/2/6' local group_ki          = '5/2/7' --------------------------------------------------------------- -- COSTANTI DI CONTROLLO --------------------------------------------------------------- local cycle_time = 120          -- secondi local filter_samples = 3        -- filtro ridotto local out_min, out_max = 0, 100 -- % local max_delta = 2             -- base rampa local deadband = 0.3            -- °C --------------------------------------------------------------- -- VARIABILI --------------------------------------------------------------- local readings = {} local last_output = storage.get('last_output') or 0 --------------------------------------------------------------- -- MEDIA MOBILE TEMPERATURA MANDATA --------------------------------------------------------------- local function moving_average(v)   if type(v) ~= 'number' then return nil end   table.insert(readings, v)   if #readings > filter_samples then     table.remove(readings, 1)   end   local s = 0   for _, x in ipairs(readings) do     s = s + x   end   return s / #readings end --------------------------------------------------------------- -- CICLO PRINCIPALE --------------------------------------------------------------- while true do   -------------------------------------------------------------   -- Aggiornamento Kp / Ki da KNX   -------------------------------------------------------------   local v = grp.getvalue(group_kp)   if type(v) == 'number' then     Kp = v     storage.set('Kp_PINT', Kp)   end   v = grp.getvalue(group_ki)   if type(v) == 'number' then     Ki = v     storage.set('Ki_PINT', Ki)   end   -------------------------------------------------------------   -- Modalità estate / inverno   -------------------------------------------------------------   local is_winter = grp.getvalue(group_mode) and true or false   if last_mode ~= is_winter then     integral = 0     last_mode = is_winter     storage.set('last_mode', is_winter)   end   -------------------------------------------------------------   -- Setpoint   -------------------------------------------------------------   local set = is_winter     and grp.getvalue(group_set_winter)     or  grp.getvalue(group_set_summer)   if type(set) ~= 'number' then     set = is_winter and 35 or 25   end   -------------------------------------------------------------   -- Temperatura mandata filtrata   -------------------------------------------------------------   local T = grp.getvalue(group_in)   local Tf = moving_average(T)   if Tf then     -----------------------------------------------------------     -- LIMITI TEMPERATURA MANDATA     -----------------------------------------------------------     local Tmax  = set + 2.0     local Tstop = set + 3.0     -----------------------------------------------------------     -- ERRORE     -----------------------------------------------------------     local error = set - Tf     if math.abs(error) < deadband then       error = 0     end     -----------------------------------------------------------     -- INTEGRALE     -- (bloccato solo sopra Tmax)     -----------------------------------------------------------     if Tf <= Tmax then       integral = integral + error * Ki * cycle_time     end     -----------------------------------------------------------     -- USCITA PI BASE     -----------------------------------------------------------     local output = Kp * error + integral     -----------------------------------------------------------     -- AZIONE FORTE SOPRA SETPOINT     -----------------------------------------------------------     if Tf > set then       output = output - Kp * (Tf - set) * 3     end     -----------------------------------------------------------     -- AZIONE PIÙ FORTE SOPRA Tmax     -----------------------------------------------------------     if Tf > Tmax then       output = output - Kp * (Tf - Tmax) * 4     end     -----------------------------------------------------------     -- TAGLIO DI SICUREZZA     -----------------------------------------------------------     if Tf >= Tstop then       output = out_min       integral = 0     end     -----------------------------------------------------------     -- SATURAZIONE     -----------------------------------------------------------     if output > out_max then       output = out_max     elseif output < out_min then       output = out_min     end     -----------------------------------------------------------     -- RAMPA DINAMICA     -- apertura veloce, chiusura controllata     -----------------------------------------------------------     local ramp = max_delta     if error > 5 then       ramp = max_delta * 4     elseif error > 2 then       ramp = max_delta * 2     end     local delta = output - last_output     if delta > ramp then       output = last_output + ramp     elseif delta < -max_delta then       output = last_output - max_delta     end     -----------------------------------------------------------     -- SCRITTURA KNX     -----------------------------------------------------------     if math.abs(output - last_output) >= 0.5 then       grp.write(group_out, output)       last_output = output       storage.set('last_output', output)       storage.set('integral_PINT', integral)       log(string.format(         "[%s] SP %.1f  T %.1f  OUT %.1f%%  ERR %.2f",         is_winter and "INV" or "EST",         set, Tf, output, error       ))     end   end   sleep(cycle_time) end
RE: Pid - admin - 13.01.2026
Most likely you need to tune P/I parameters. Create trend logs for both temperature value and valve output and see how the system behaves with different parameters.
RE: Pid - Michael - 14.01.2026
First of all, thank you for your reply, but it seems that even raising the P/I parameters doesn't improve.
RE: Pid - admin - 14.01.2026
For tuning the parameters do the following:
1. Use PID script from our KB: https://kb.logicmachine.net/scripting/pid-thermostat/
2. Create a trend log for output value and current temperature
3. Set ki and kd to 0
4. Keep the setpoint constant
5. Adjust kp so the temperature oscillates around the setpoint
6. Let the system run for some time
7. Record the time between each oscillation (Tu)
8. PID parameters can be calculated using the following formula, where Ku is the kp value from the step 5.
kp = 0.6 * Ku
ki = 1.2 * Ku / Tu
kd = 0.075 * Ku * Tu
You can try other coefficients to further tune the system: https://en.wikipedia.org/wiki/Ziegler%E2%80%93Nichols_method
RE: Pid - Michael - 15.01.2026
Hi, thanks for the valuable advice, now it seems to be starting to work quite well, I need to give it a little more fine tuning, but compared to before this is already an excellent result. I'm posting the logs. Thanks a lot, good work.