Strange modbus scaling - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: Strange modbus scaling (/showthread.php?tid=6354) |
Strange modbus scaling - Ceros2112 - 17.03.2026 Hello, I have a modbus device that scales values in a strange way and I don't know how to make it work, if possible, with LM5. Basically the formula is: (value+5)*2+30, in other words it reads values from -20 to 100 and represents values from 0 to 240 so, for example, if the value read by the instrument is -20, via modbus I will read 0. Any ideas on how to integrate it in a json modbus profile? RE: Strange modbus scaling - admin - 17.03.2026 value_base = -20 value_multiplier = 0.5 Formula: value = value_base + value * value_multiplier value = -20 + value * 0.5 If read value is 0 the resulting value is -20. If read value is 240 the resulting value is 100. RE: Strange modbus scaling - Ceros2112 - 17.03.2026 thanks! I've tried it before but I must have done something wrong |