Pool Modbus RTU - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: Pool Modbus RTU (/showthread.php?tid=727) |
Pool Modbus RTU - Igor68 - 09.04.2017 Hello, how can I reduce the polling time for the Modbus RTU protocol? I only have one module on the network RS-485, it allows a polling time of 100 ms and I would like to put 100 ms to increase the speed instead of 1 second. Is this possible? RE: Pool Modbus RTU - Erwin van der Zwart - 09.04.2017 Hi, If you use a resident script then just set the script interval to x seconds, if you use the modbus template then you can set the polling interval on the device by double click the device and set the interval. BR, Erwin RE: Pool Modbus RTU - Igor68 - 09.04.2017 Hi, the tab can be minimized only 1 second. And how to make less than 1 second? RE: Pool Modbus RTU - Erwin van der Zwart - 09.04.2017 Hi, Create a resident script with interval 0 and read the device from this script and include a os.sleep(0.1) to reduce the interval from max cpu speed to 100ms. I wunder if this won't give issues when the object is refreshed at this interval... I think that is the reason why the template has the lowest option to set it to 1 sec.. But you can always try.. BR, Erwin RE: Pool Modbus RTU - Igor68 - 09.04.2017 thanks, I'll try I tried, unfortunately, the reaction rate is small RE: Pool Modbus RTU - admin - 10.04.2017 Which device do you need to poll this often? If you only have one device and you don't need to write to it, then a script is be a better solution. RE: Pool Modbus RTU - Igor68 - 10.04.2017 Hi, The device has only one digital input-output terminal of 8 channels, controls lighting, so the response delays are critical RE: Pool Modbus RTU - Erwin van der Zwart - 10.04.2017 Hi, This is why they invented KNX (: BR, Erwin RE: Pool Modbus RTU - Igor68 - 11.04.2017 Hi, So after all, the RS485 interface has a polling capability of less than 100 ms and then the response rate is good. I have other equipment running fast with the modbus RTU. It would be nice if the user himself could set the parameters according to the protocol capabilities)))) |